    Ice-O-Matoc ICE1403 Not making ice

    I have an Ice-O-Matic ICE 1403 (Cuber, Remote Condensor ) that recently started acting up. It makes ice, but only when it is above 70 degrees outside. It is inside a shop that stays between 50 and 70 degrees year round, and it used to make ice 24 hours a day. I have experience with commercial and residential HVAC, but this ice machine is giving me fits. I have had two other companies come work on the machine. One replaced the harvest assist motors, and both have come up with dozens of reasons why it is acting up but still can't get it to work correctly. They both have about 4 hours labor invested each with no results. Any ideas?

  2. #2
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,308
    Anyone throw a set of gauges on it?
    Every customer you take for granted today will be someone else's tomorrow.

  3. #3
    Yes, both companies say the pressure looks good. I am in Texas and we haven't had much warm weather for the past couple of months, so of course when they show up it is close to 70 outside and making ice. When it cools down in the evenings below 65 or so, the water continues to flow but it no longer freezes.

  4. #4
    Join Date
    Apr 2007
    Location
    Scottsdale,AZ
    Posts
    80
    Check the headmaster.

  5. #5
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,308
    Quote Originally Posted by mizzterclean View Post
    Check the headmaster.
    Exactly- thats what i was getting at. Something is wrong with your outside unit.
    Every customer you take for granted today will be someone else's tomorrow.

  6. #6
    What do I need to check with the outside unit? By the way, thank you both for the help! It is greatly appreciated.

  7. #7
    The machine made almost 300lbs. of ice today. Worked great from 1 p.m. Until 8 p.m. The temp was 70 when it started making ice and it quit when the outside temp came down to 65. Went into harvest every 15 minutes.

  8. #8
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,428
    It sounds to me like the Headmaster is OK. Most likely the system is just low on charge.

  9. #9
    Join Date
    Dec 2010
    Location
    Woodbridge Twp, NJ
    Posts
    1,308
    call your pro and have them come first thing in the morning.
    Every customer you take for granted today will be someone else's tomorrow.

  10. #10
    Join Date
    Jan 2011
    Posts
    135

    basics

    Iceomatic ice machines are tricky and they also have a 800 number tech support out of colorado I think. the first thing I would do is recover the refrigerant and weigh in the exact amount of the nameplate, but i would vacuum the system down to remove any moisture or anything like that, i would also check the condenser split

  11. #11
    Join Date
    Apr 2004
    Location
    NJ
    Posts
    155
    Excuse my rusty-ness. To my recollection, Ice - o -matic machines go into harvest based on low pressure. At a cooler outdoor ambient, pressure would be lowered in a shorter amount of time, which would initiate a pre-mature harvest. In my opininion, the charge is low.

  12. #12
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,428
    Mt guess that it's low on charge is based on how the Headmaster works in the system and its relationship with ambient temperature and the system charge.

    R404A icemaker systems typically use a Headmaster valve which is set at about 210 psig, or about 90 Deg F condensing temp, to flood the condenser with liquid by bypassing discharge gas to the receiver to maintain head pressure. This additional liquid refrigerant must come from the reserve in the receiver. If there's not enough refrigerant in the system to adequately flood the condenser, the receiver will run dry and the TXV will be starved.

    It's probable then that at around 65 Deg F ambient the Headmaster on this system is trying to flood the condenser and there's simply not enough gas to accomplish that.

    If the system has worked OK in the cold weather previously, then it would be wise to look for a leak someplace.

  13. #13

    Ice-O-Matic Tech Service

    I am a Tech with Ice-O-Matic. Feel free to give us a call at 800-423-3367. Press option 3.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event