    Follett Horizon argggh. Long, but bear with me.

    I don't work on ice machines much, but I think I have this one all screwed up. We had one going off on head pressure. I restarted the unit and checked it and had 300#. It's a water cooled Follett Horizon. Based on the touchy feely test I had cool water going in, I'd say about 75* and I had hot (not warm) water coming out. The strainer was clean. I stupidly tried to adjust the water regulater valve and it didn't help. (You know the water regulator valve that has the big piece of tape over it that says "do not adjust?" Yeah, that one.)

    So... to buy time, I told them I suggest cleaning the condenser and getting a new water regulator. I came back and to clean it and change out the water regulator. I only took out about 9 oz of gas where the total charge is 15oz. Hmm. I put in the new regulator and leak check. I can't find anything. I start the unit and attempt to charge and I can only get the whole charge in before my head starts going up to 250# What's wrong??? Still hot water coming from the condenser outlet. It's making ice, so I'm going to leave it for now.

    While looking at the unit, I see 1/4" OD copper feeding the condenser water lines feeding it where the connections are 1/4"npt. Ha!, I figure I have it. Tell them I'm going to repipe it, I think that's the problem....

    I come back and repipe it. It doesn't help. I come to find out that I put the valve in wrong. I put the new valve in the same way as the old valve. I have since thrown out the old valve, so I can't verify. But I know I'm right. Ha! I figure I have it again.... Nope. I flip the valve around. I can get the whole charge in now, but my head is 325 -350. The rise across the condenser is way better though. What's going on here?? I'm thinking maybe noncondensibles?

  2. #2
    Join Date
    Jan 2010
    Posts
    6,816
    What refrigerant & what was your water pressure ?

  3. #3
    Join Date
    Apr 2006
    Posts
    329
    404a and 90# water pressure. 150# is max.

  4. #4
    Join Date
    Jan 2010
    Posts
    6,816
    Did you get a low side pressure reading ?

  5. #5
    Join Date
    Jan 2010
    Posts
    6,816
    Whats the model # ?

  6. #6
    Join Date
    Jan 2010
    Posts
    6,816
    Looking at there 400 & 1000 series i see a 90* max. water temp. & 70 psi max. water pressure.

  7. #7
    Join Date
    Apr 2006
    Posts
    329
    hcc1000w

  8. #8
    Join Date
    Apr 2006
    Posts
    329
    that's potable water, condenser water is 150

  9. #9
    Join Date
    Jan 2010
    Posts
    6,816
    Quote Originally Posted by dudeabides View Post
    that's potable water, condenser water is 150
    Yes that's correct i looked up the model and found this info.
    70*F water = 225 psi.
    80*F water = 231 psi.
    Factory set @ 230 psi. +/- 15 psi. @ 70*F
    Also the line size is correct @ 1/4"
    What happens when you adjust the water regulator ?

  10. #10
    Join Date
    Apr 2006
    Posts
    329
    3/8 od. Nothing happens when I adjust it. Tech support has told me that if you adjust the reg, it should be replaced. That doesn't make sense to me.

  11. #11
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    76
    I agree because if it has been working fine before and you have to adjust it to make it work again with different settings then something has obviously failed in the valve to mess it up.

  12. #12
    Join Date
    Jan 2010
    Posts
    6,816
    Quote Originally Posted by sgagne199 View Post
    I agree because if it has been working fine before and you have to adjust it to make it work again with different settings then something has obviously failed in the valve to mess it up.
    Or water pressure / temperature has changed.

  13. #13
    Join Date
    Jan 2010
    Posts
    6,816
    Quote Originally Posted by dudeabides View Post
    3/8 od. Nothing happens when I adjust it. Tech support has told me that if you adjust the reg, it should be replaced. That doesn't make sense to me.
    What did tect support say about cleaning the water condenser ?

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event