    Hmm carrier 19DH oil problems

    I have a problem with a 19dh R-11,450 ton, motor style 31, someone turned the condenser water setting up to 100 degrees,after this happen when its running the oil level goes out of the sight glass,have to keep adding oil to operate, i think they blew the lab seal, but not sure witch one, the thrust or the other, can anyone help me with this problem.

  2. #2
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Sounds like the laby between thrust and impeller off of info given. Regardless it's got to be inspected and found. Slider back and check your clearances, I would be some what concerned with the thrust condition. And according to unit history and time constraints, complete bearing inspection


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Jan 2011
    Location
    michigan
    Posts
    9
    Post Likes
    Thread Starter

    Hmm 19dh

    thanks for the info, the chiller was completey overhauled last spring by carrier,all new bearings

  4. #4
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Good luck


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Oct 2011
    Location
    La.
    Posts
    325
    Post Likes
    How fast does the oil level drop and what is the load on the machine when this is happening. also what is the temp of the condenser water. do not jump to a slide back. It may be something simple.

  6. #6
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    322
    Post Likes
    Before pulling compressor back, pull handhole cover and check wiring to motor temperature sensor where it pentrates wall between motor and oil sump. Many times these come out and create oil problems.
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  7. #7
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    True to both of you, out ran myself


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Aug 2016
    Location
    South Africa
    Posts
    8
    Post Likes
    Hi ricktys09


    Sorry but we currently have a very similar problem of oil not returning to sumps, we have check all the feeds for blockage but nothing found. The oil moves to the Volute but due to the amount of oil the return to sump is small and we end up draining the oil sump to the volute.

    I know its been a while but was your issue resolve and what was the findings?
    I have posted all the interim fault finding on forum.