AS/Trane factory installs start assist kits on their heat pumps with scroll compressors, and has called for the addition of them to scroll equipped AC units, used for low ambient cooling, for a number of years.
Since scroll compressors have more mechanical friction than recips to overcome when starting, they use larger motors, with higher LRA, than similar capacity recip compressors.
Because of the higher start-up current, the motors in scroll compressors, as well as the contactor, etc., benefit from start assist components even more than recips.
This is especially true when the compressor is cold, due to the increased friction from the oil thickening, and contraction of the metal parts.
I think some of the "debate" over hard start kits on scrolls stems from past, maybe current, cautions from various sources about using them on scroll compressors that have mechanical problems that cause them to stick.
Those cautions have often been strongly worded, or even labeled as warnings.
It has always been common with mechanically stuck recip compressors to get more life out of them by installing a hard start kit when one is found not starting due to a mechanical issue. It can't hurt to try it, and compressors often run that way for years.
Scroll compressors are mechanically very different than recips, and due to the nature of how the scroll mechanism works, and the tight tolerances, just need to be replaced if they are mechanically sticking enough to not start without a start assist.
Adding a start kit to eek some more life out of a recip with mechanical issues typically won't result in anything worse than further mechanical damage.
Adding a start kit to a scroll compressor with mechanical damage is a high probability path to a burnout.
Never hesitate to add a proper start assist to a scroll compressor to reduce light dimming due to voltage drops on startup, and/or stress on the motor windings, or to help with starting in very low ambient temperatures.
I wouldn't install one on a scroll compressor that is mechanically stuck though, unless it is just to get it going for a day or two until you get back out to replace it.
I'm finding they may with these new coils that do not equalize. I typically install their 13 seer rectangle units and they have not been coming with start components. A few years ago when the 13 was the next up in line they did come with them. At that time I was under the impression that they were added along with a HP cutout because they carried a ten year parts/compressor over the 1/5 on the base model.
I guess in the end its always cost. The same reason they start putting in contactors for 15 cents less then the ones with nice lugs!
yes...very informative. thank you
Agreed, very good information. Thanks for posting that.
Sent from my PG86100 using Tapatalk
anybody use the starter pow-are-paks with any problems?
The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....
¯`·.¸¸ .·´¯`· .¸>÷÷(((°>
`·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>
.·´¯`· .¸>÷÷(((°>
LMAOSHMSFOAIDMT
I think the "not advised" wording is a little misleading.
What the scroll guys are saying is that because a scroll starts basically unloaded, there should be no need for a start assist device. However, there are times when one is indeed indicated. The scroll motor is electrically identical to a recip motor. Only the method of compression is the difference when it comes to loading on startup.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
There are a lot of informative videos on youtube, just search refrigeration compressors. I also like the 5-2-1.
Challenge yourself, take the CM test --- Certificate Member since 2004 ---Join RSES ---the HVAC/R training authority ---www.rses.org
It's a smoother, more gradual start because the scrolls take several revolutions to build a pressure that is greater than the discharge line pressure, whereas a recip builds that pressure in a stroke or two of the pistons, which is often one or two revolutions, so the load on the recip motor is much steeper from rest to running at RLA.
[Avatar photo from a Florida training accident. Everyone walked away.]
2 Tim 3:16-17
RSES CMS, HVAC Electrical Specialist
Member, IAEI
AOP Forum Rules:
Thanks for all the feedback , help and advice. I really had not heard of those 3-2-1 kits and hope to find a parts place around me that handles them. I also hope there is enough room in these downsized control sections to install them.
The internal pressures on the pumping mechanism in a scroll compressor equalize nearly instantly when it turns off because there are no discharge or suction valves to prevent it.
There is a check valve in the discharge outlet of the compressor shell to prevent the system pressures from equalizing through the compressor, but there is no pressure difference across the actual pumping mechanism, so scroll compressor always start fully unloaded.
"5-2-1"
so I meter the start caps when diagnosing and find some of them bad, I sometimes reuse the existing pot relay and just change the cap. Keep some in my van. Usually the relay is still good. Anyone object to this, I am talking about getting a compressor up and running when it just won't start.......meter goes up and then down on a start cap, I crimp a terminal end on the resistor and reconnect to the terminal when done. What would happen if the resistor was left unattached?
I guess I will be throwing away all my super boost. Great thread. This is why I am here every day. Very informative. Thanks for all the info gentleman.