    Trane wiring diagram

    Hi,
    Can anyone point me to where I could find a wiring diagram for a Trane TWE036c140a0. The fan motor won't stop running, and I've got a mess of wires around the relay.
    My Best Always,
    Ray in Tex

  2. #2
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,848
    Fan manager?

  3. #3
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,789
    how old is it?

  4. #4
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,789
    heres one document for it
    Attached Images Attached Images

  5. #5
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,848
    Quote Originally Posted by gravity View Post
    heres one document for it
    Yep, fan manager!

  6. #6
    It's about 15 years old. It has a 10 pin relay, and I just want to make sure wiring is correct before I condemn relay. It has obviously been worked on over the years; many pigtails.

  7. #7
    Join Date
    Jun 2004
    Location
    tyler texas
    Posts
    27
    Quote Originally Posted by KB Cool View Post
    Fan manager?
    cut the red cap pull relay out rewire g and common to relay all the other stuff the same will work

  8. #8
    Join Date
    May 2004
    Location
    Frederick, MD
    Posts
    924

    What if

    Quote Originally Posted by ctn View Post
    cut the red cap pull relay out rewire g and common to relay all the other stuff the same will work
    there is more than 1 red wire?
    GO NAVY, BEAT ARMY!

    A DECADE OF DOMINANCE! +2

  9. #9
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    2,848
    Quote Originally Posted by ctn View Post
    cut the red cap pull relay out rewire g and common to relay all the other stuff the same will work
    Yeah, you can do that. But, i'd just change the part, charge accordingly and keep the 80 second fan off delay as the manufacturer intended. In a pinch, your way will work too.

  10. #10
    Hey guys,
    Thanks for input,
    took red off (24) and cool does energize and fan comes on. It doesn't run all the time. Heat, however does not bring fan on. There is no sequencer, but contactor. High voltage has been messed with. My schematic does not include wiring diagram for factory items. Could someone pls include diagram or suggestions. Wiring old electric furnaces from scratch is not my strength. I don't understand how from what I see how fan could come on with heat with the 940 relay. What signal is going to make fan come on from 940 in heat when g and common energize coil?

  11. #11
    Join Date
    Jun 2004
    Location
    tyler texas
    Posts
    27
    tstat must call for fan on in heat with this unit was the stat changed? if so prodram for it to turn on blower in heat

  12. #12
    Thanks for suggestion, will check, trying to find install manual for this Hunter therm to check settings, but element contactor is not engaging in heat either with 27 vac to heat terminal.

  13. #13
    Join Date
    Dec 2011
    Location
    Georgia
    Posts
    18
    If i had $124.00 for every time i have seen one of those old time delay relays from trane do that i would be................ my boss? hee hee.
    They also have another one on some of the 2/4TGB models that doesn't resemble a traditional relay at all, more like a small solid sate device, i have seen these do the exact same thing. over engineered garbage... what was wrong with just a regular relay anyway?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event