I have a problem with a 19dh R-11,450 ton, motor style 31, someone turned the condenser water setting up to 100 degrees,after this happen when its running the oil level goes out of the sight glass,have to keep adding oil to operate, i think they blew the lab seal, but not sure witch one, the thrust or the other, can anyone help me with this problem.
03-10-2012, 08:33 AM #2
Sounds like the laby between thrust and impeller off of info given. Regardless it's got to be inspected and found. Slider back and check your clearances, I would be some what concerned with the thrust condition. And according to unit history and time constraints, complete bearing inspection
03-10-2012, 08:42 AM #3
- Jan 2011
- michigan
- 8
19dh
thanks for the info, the chiller was completey overhauled last spring by carrier,all new bearings
03-10-2012, 08:44 AM #4
Good luck
03-10-2012, 04:03 PM #5
- Oct 2011
- La.
- 211
How fast does the oil level drop and what is the load on the machine when this is happening. also what is the temp of the condenser water. do not jump to a slide back. It may be something simple.
03-10-2012, 07:44 PM #6
- Sep 2011
- Northwest Louisiana
- 155
Before pulling compressor back, pull handhole cover and check wiring to motor temperature sensor where it pentrates wall between motor and oil sump. Many times these come out and create oil problems.
A LITTLE BIT OF STUPID GOES A LONG WAY!
03-11-2012, 04:59 PM #7
True to both of you, out ran myself