  1. #14
    Join Date
    Oct 2011
    Location
    La.
    Posts
    282
    You are using the wrong tools. Your company needs to spent the money if they want to work on chillers. I feel for you.

  2. #15
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Lol no doubt, it's been a fun ride. Getting too old for this, still here trying to get parts coming. Gotta love them emergency all nighters. It's Friday and everyone is gone. Thrust bearing wiped pretty bad, got a call in with RCD.


    Sent from my iPhone using Tapatalk
    Attached Images Attached Images

  3. #16
    Join Date
    Oct 2011
    Location
    Upstate NY
    Posts
    55
    How does the impeller look? Did it get by unscathed???

  4. #17
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Yes, impeller looks good. Replacement parts coming in. Going to head that way and check and clean out oil sump


    Sent from my iPhone using Tapatalk

  5. #18
    Join Date
    Oct 2011
    Location
    Upstate NY
    Posts
    55

    Talking

    Your profile states you've been in the field for a while but mainly with "low pres" experience. Not knowing how much exp. you have with the XR's, I want to give you a heads-up that the XR's have a very specific impeller spacing procedure. I actually found the pertinent Carrier SB (SB C0405) performing a web search (look for "19XR/XRT impeller spacing procedure"). Also know, that in order to set/measure the proper thrust brg. clearance, a tool is required to be installed over the high speed shaft and held in place with washers and impeller bolt (a pipe cut to proper length can be used) to simulate the impeller installed on the shaft OR A FALSE READING WILL BE MEASURED... Good Luck...

  6. #19
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Thanks for the heads up, I found that service bulletin today. Yes it will be my first high pressure 19 series. Very similar to the Old D machines. I take it that the gear set is not match ???


    Sent from my iPhone using Tapatalk

  7. #20
    Join Date
    Oct 2011
    Location
    Upstate NY
    Posts
    55
    There are many similarities between the 19D's and 19X's but the gearsets are not the same... Any updates?

  8. #21
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Yes, replaced the Thrust Assm. and recalculated impeller clearance. Cleaned out the oil sump and pump, replaced all filters and oil. Started her up and checked operation, found out customer has a flow issue that is being addressed and a misunderstanding of the chiller's operation. More will soon follow, very busy right now


    Sent from my iPhone using Tapatalk

  9. #22
    Another way, you can recover the existing refrigerant gas to empty cylinders by vacuuming the empty cylinders. After cylinders are in vacuum pressure, you can connect the hose through the 1" valve; below the cooler shell.

    For this purpose you might need 20 cylinder of 56Kg.

  10. #23
    Sorry, I dont really get it. What do you meant by "customer has flow issue"?

  11. #24
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,093
    Quote Originally Posted by henpeck View Post
    Ok as I'm setting here transferring refrigerant, what would be the equipment you would use size 5 - 19 xr with a 1360 # charge of 134a. To inspect your thrust bearing. ????


    Sent from my iPhone using Tapatalk
    You mean u didn't just blow it into a bucket?
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  12. #25
    Join Date
    Mar 2012
    Location
    Corpus Christi Texas
    Posts
    3
    United refrigeration will rent you a pump out. I usually use a nrp liquid pump and then pull vapor once liquid is transferred. And make sure you have water flow when you get to freezing sat temp.

  13. #26
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    I tried blowing the oil charge in the bucket, but was over come with oil/refrig vapor at first and it made me light headed. Not to forget about the oil that started blowing up out of it everywhere, I guess should have throttled that 1/2" angle back a-little. :-)....on a serious note: the refrigerant was supposed to be already transferred to the high side when I got to the job after hours. Our shops high pressure recovery was down and I had no idea how much was transferred at that time. But yes I should have opened up united refrig. and got their rental equip and been fine. It just gave me time to get and set up rigging. To cover the low flow issue, after repair I started the chiller and started checking and trouble shooting I found out real fast that there wasn't very much load for the chiller and it was doing a 10degree delta T at like 48% rla. Got flow issue and building automation control problem straightened out.


    Sent from my iPhone using Tapatalk

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event