Thread: Ys chiller No oil return

  1. #1
    Join Date
    Jan 2012
    Posts
    7
    Post Likes

    Hmm Ys chiller No oil return

    I have four 300 ton ys s2 york chillers,I got the oil results back and #2 and #3 chiller needed an oil change.So we changed the oil in #2 and it ran for 24 hours and it seemed to be ok so we did the oil change in #3 chiller,then on Saturday the weekend crew said #2 shut down on low seperator oil,when I came in it looked like there was enough oil in the sump so I started it back up and it ran for about 15 min and shut down on low oil.So we checked out the Eductors and they were ok we had already changed the eductor filters so we ruled that out.
    Whats really got me stumped is that I started up chiller 3 today and it is doing the same thing that #2 is. Both chillers were running fine before oil change and now are having the same problem.
    Like I said they are york ys -s2 chillers and the book I have says to use 10 gallons of York type C oil.
    Am I missing something?
    any thoughts?
    Thanks

  2. #2
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    What is you entering Condenser temps been running?


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Condenser water temps getting too low can cause you problems.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Make sure condenser water temps are right, and tower fans operating properly


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    low partial load, condenser water temperature low, low water flow

  6. #6
    Join Date
    Jan 2012
    Posts
    7
    Post Likes
    Thread Starter
    I have tried setting my tower fans at different speeds and it does the same thing if the CT water is 75 or 95,With a higher head press the oil does return but it leaves almost as fast
    I did notice that my discharge temp is low about 15 DSH and my slide valve never got farther than 40% and the water setpoint is 45 and it never got lower than 47

  7. #7
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Check your flows, odd that it's happening to
    Most of them. Must be WD? Chill wtr and condenser wtr make sure they have the bldg aud . Did you say you are having to run tower fans manually?


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    Sorry I can't do more than one thing at a time. Verify proper chill wtr flow. Make sure they have there controls working properly


    Sent from my iPhone using Tapatalk

  9. #9
    Join Date
    Jan 2012
    Posts
    7
    Post Likes
    Thread Starter
    I don't have to run fans on Man. I just did to get temp up

    What I can't keep asking is why they ran fine before oil change and now shutting down.nothing else was done???

  10. #10
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    That you know of, did you verify oil charge plus how much did you remove from each ch


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    oil charge for these machines is 10 gallons. that version is the machine?

  12. #12
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes

    York YS

    What refrigerant is the Chiller using ? Because some are R22 and some are R134a
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  13. #13
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes

    York YS

    Reason I ask R22 takes C-oil and R134a takes K-oil just thought I would ask this stupid question.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  14. #14
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    Quote Originally Posted by york56 View Post
    What refrigerant is the Chiller using ? Because some are R22 and some are R134a
    your question is not stupid. is correct that questions

  15. #15
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes

    York YS

    Quote Originally Posted by servicetrane View Post
    your question is not stupid. is correct that questions
    I guess we will have to wait and see what the answer is.
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  16. #16
    Join Date
    Jan 2012
    Posts
    7
    Post Likes
    Thread Starter
    I believe I wrote in my original post That I had a YS-S2 chiller that we put in 10 gallons of york type C-oil
    I got about 8 to 8 1/2 gallons out that was with a filter change

  17. #17
    Join Date
    Jan 2012
    Posts
    7
    Post Likes
    Thread Starter
    I should add that before I left for the day,,I jumped the float switch raised the condenser temp/high side pressure and I get plenty of oil back to the separator but it leaves just as quick...now it seems to be more of a surge type of problem

  18. #18
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes

    York YS

    So you still have not answered the question R22 or R134a because S2 is either refrigerant so which one is it ?
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  19. #19
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,752
    Post Likes

    York YS

    Here let try this since obviously I don't know anything , how about posting all your operating data let see if you can do that so we all can take a better look see !
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  20. #20
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    562
    Post Likes
    sequence E, works or r-22 or R134a

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •