American standard freedom 80
I have a 190 -30 limit switch to replace .. Does this switch activate the blower when the temp reaches 160 and when it exceeds 190degrees ??
-
03-07-2012, 08:58 AM #2
Not sure of that unit but unless its a dinosaur the limit switch doesnt activate the blower. Its a safety.
It will open at 190 and close at 160
-
03-07-2012, 09:02 AM #3
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
03-07-2012, 10:24 PM #4
Guest
- Join Date
- Feb 2011
- Posts
- 31
-
03-08-2012, 12:19 AM #5
Yup thats just a safety. Like said above opens at 190 and closes at 160. For the fan, that is timed ON and OFF by the board.
-
03-08-2012, 09:27 AM #6
I can't picture that furnace but on many units, probably most all today, if that limit opens it will also power on the blower and often the inducer as well.