    The magnetic contactor has 4 wires on it. The top 2 wires burnt off and started a mini fire in the system. Burnt the contactor, circuit board, and burnt/melted the TXV sensing bulb tubing. What would cause these wires to burn like this? I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.

    Any idea's why this may happen?

  2. #2

    Dead Ice Machine?

    Originally posted by hvacsteve82
    .... I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.
    If this machine needs my services, let me know soon. I anticipate taking a trip to Wallkill in the next month or two.

    Fred


  3. #3
    Join Date
    Nov 2005
    Location
    Milwaukee, WI
    Posts
    68
    Originally posted by hvacsteve82
    The magnetic contactor has 4 wires on it. The top 2 wires burnt off and started a mini fire in the system. Burnt the contactor, circuit board, and burnt/melted the TXV sensing bulb tubing. What would cause these wires to burn like this? I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.

    Any idea's why this may happen?
    It sounds like the compressor may have died, and shirted out, hard to really tel unless you see it inperson, and trace the wires around.

  4. #4
    Join Date
    Jan 2005
    Location
    Orange County, New York
    Posts
    1,459

    Re: Dead Ice Machine?

    Originally posted by ice machine undertaker
    Originally posted by hvacsteve82
    .... I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.
    If this machine needs my services, let me know soon. I anticipate taking a trip to Wallkill in the next month or two.

    Fred


    Who are you Fred? Do I know you? How do know this is in Wallkill...and i'm not talking about the Wallkill near Middletown.

  5. #5

    Re: Re: Dead Ice Machine?

    Originally posted by hvacsteve82


    Who are you Fred? Do I know you? How do know this is in Wallkill...and i'm not talking about the Wallkill near Middletown. [/B]
    I have a cousin in Wallkill (north of Walden) who needs a visit.


  6. #6
    Join Date
    Mar 2005
    Location
    burlington county n.j.
    Posts
    9,743
    wires burning off could have been something as simple as a loose connection.

  7. #7
    Join Date
    Jan 2005
    Location
    Orange County, New York
    Posts
    1,459

    Re: Re: Re: Dead Ice Machine?

    Originally posted by ice machine undertaker
    Originally posted by hvacsteve82


    Who are you Fred? Do I know you? How do know this is in Wallkill...and i'm not talking about the Wallkill near Middletown.
    I have a cousin in Wallkill (north of Walden) who needs a visit.

    [/B]
    Funny thing is that is the Wallkill/Walden area the ice machine is located. Amazing.

    Cusotmer is going to replace ice machine. I talked to them today.

  8. #8

    Re: Re: Re: Re: Dead Ice Machine?

    Originally posted by hvacsteve82

    Funny thing is that is the Wallkill/Walden area the ice machine is located. Amazing.

    Customer is going to replace ice machine. I talked to them today. [/B]

    I spoke with my cousin today. The anticipated date of travel is on or about June 1. If the ice machine needs a proper burial, my email is in my profile.



    Fred

  9. #9
    Join Date
    Jan 2005
    Location
    Orange County, New York
    Posts
    1,459
    Haha, It should be replaced by then. If you want it i'll save it for you possibly, unless the bossman wants it for some odd reason.

  10. #10
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,370
    Originally posted by hvacsteve82
    The magnetic contactor has 4 wires on it. The top 2 wires burnt off and started a mini fire in the system. Burnt the contactor, circuit board, and burnt/melted the TXV sensing bulb tubing. What would cause these wires to burn like this? I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.

    Any idea's why this may happen?
    Here's my theory:

    On the contactor the bottom terminals go to the coil and the top two (11 and 12, I think) are your power to the compressor. The compressor has an external overload which I suspect got welded closed, possibly due to repeated trips caused by a failed start cap and/or relay.

    In my experience, a loose connection will usually burn locally, not over the entire length of the conductors, so I believe its not that.

    I would expect the compressor is fried as well as a result.

  11. #11

    tech

    Quote Originally Posted by hvacsteve82 View Post
    The magnetic contactor has 4 wires on it. The top 2 wires burnt off and started a mini fire in the system. Burnt the contactor, circuit board, and burnt/melted the TXV sensing bulb tubing. What would cause these wires to burn like this? I am giving the customer a quote on a repair, but its almost not worth repairing after all the money will be spent fixing this unit.

    Any idea's why this may happen?
    hey Steve i guess my first question to you will be how old is this unit? that occur to me once a while back i called tech support but the only logical answer that the have was that the contactor had a bad inside contacts which makes the contactor to super over heat cousing posible problems to near by electrical components. this happens 1 in a 1000 contactors its a manufactures problem.
    your customer should change that unit.
    good luck!!!:

  12. #12
    Join Date
    Jan 2005
    Location
    Orange County, New York
    Posts
    1,459
    LOL they changed it out 4 years ago...thats how old this thread is!