5 Ton AAON Unit
In the attached document could someone explain why Aaon has the static pressure and TSP labeled the same? I thought static pressure and total static pressure where two different readings.
-
03-06-2012, 09:43 AM #2
Regular Guest
- Join Date
- Feb 2012
- Location
- Upstate SC
- Posts
- 84
I think they are just saying that the unit will deliver 2000 CFM at that SP. The total SP is what the unit will deliver out the box. Once you attach it to the duct work its performance will be cited in external static pressure which is what you probably thinking of.