03-09-2012, 05:41 AM #53
OK, great. Heat transfer is taking place.
I don't need gauges to tell me that. My hand will typically tell me that there is a temperature difference between the discharge and the liquid line.
Still doesn't tell me what I NEED to know about the system.
That the TXV had a solid column of liquid.
Since it doesn't tell me that, it is NOT a charging metric.
-
03-09-2012, 06:48 AM #54
Regular Guest
- Join Date
- May 2011
- Location
- Chas.,WV
- Posts
- 30
I believe a case could be made for and against the location of the moisture indicator on the liquid line. All the racks that I work on have the SG located downstream of the drier. Basically as you have indicated, the purpose is to ensure a solid column of liquid , at that point , at least. My point is that used as as part of the diagnosis the SG is valuable.....but , to make a final decision only on a full or bubbling SG will often lead you down the wrong path.
-
03-09-2012, 08:27 AM #55
Sight glass should be installed downstream of the filter drier. You can figure out if you're short on gas or the drier is plugged it's not that difficult. Best place for the glass would be at the txv. On some racks you will get bubbles in the sight glass. You will get what looks like a half full glass sitting there. You will get rivering. You don't want to use that as a charging indicator. I think on a large vertical receiver there is turbulance going on in the bottom from the liquid being dumped in the top.
Now if you're working on a tyler equalizer rack then your sight glass is a proper charge indicator. You have to be careful.
-
03-09-2012, 08:40 AM #56
Hes talking about temperature/pressure correlation. The machine must be idle. It must also be pumped down so your not getting a mixed pressure reading from the liquid that may still be in the liquid line inside the conditioned area. Take your pressure and temperature and find it on the chart, just like you would on a container containing an unknown refrigerant.
Ive tried it and found its still hard to tell, especially on an old r-12 or 502 cooler where a number of refrigerants are very close as far as press/temp correlation.
If the refrigerant is known as it supposedly is in this instance then non-condensibles would cause the pressure of the r-22 to not correlate with the temperature.Last edited by ar_hvac_man; 03-09-2012 at 08:43 AM. Reason: more info
-
03-09-2012, 10:09 AM #57
On smaller equipment and singles compressor walk-in boxes I usually see it's order as
1) Filter/Drier
2) Liquid Solenoid Valve
3) Liquid/moisture indicator
Usually all the above items are located inside the condensing unit.
The sight glass should be full. If you see any bubble in the glass, you would want to take action and look for...
1) Short on charge
2) Rapid Liquid pressure/temperature fluctuations (fan cycling)
3) Restricted filter drier
4) Restricted liquid solenoid valve
If it's a pump down system, and you charge to a clear sight glass...you need to make sure the system can pump down without tripping the high pressure control.
Some systems receivers can't hold the pump down. You could re-locate the liquid solenoid from the condensing unit and put it closer the the evap coil. You gain some additional volume to store pump down in the liquid line.
I'm getting off track...
Whether the sight glass is installed before or after the filter, it is a charge indicator. But when installed after the filter, it becomes so much more. and can alert you of a few extra systems problems.
-
03-09-2012, 10:54 AM #58
Professional Member
- Join Date
- Dec 2011
- Location
- pensacola fl.
- Posts
- 88
-
03-09-2012, 11:18 AM #59
Professional Member
- Join Date
- Dec 2011
- Location
- pensacola fl.
- Posts
- 88
Lets look back. You told the guy to charge the system and move on. Did you place your hand on the liquid line? All I saying is head press is one of many observation a tech can use. Head has to referenced to something, normally that is OA. What I would be looking for is not that there is a difference, but the degree of difference between both measurments.
-
03-09-2012, 08:27 PM #60
Professional Member
- Join Date
- Oct 2011
- Location
- midwest
- Posts
- 58
Phase Loss, good info... Thats what what I found on this condensing unit... From simple question. Why my head pressure was flacuating. I learned a lot more...