    Chiller 5-year maintenance question

    Hi all, chiller maintenance question.

    I have budgeted for 5-year maintenance for a chiller at 1 of my props. 1 HVAC vendor provided me w/a “tear-down” quote – items like O-rings replacements, etc. that I have seen for other 5-year maintenance. Another vendor said that the type of chiller does not require tear-down.

    It is an 80 ton Trane unit w/screw compressors – the vendor that said tear down is not applicable said that because it is a “screw” unit, rather than centrifugal, just checking oil, brushing tubes is enough.

    Any comments welcome. thanks

  2. #2
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,668
    What kind of O-rings? Maybe the rings are for the condenser head. As far as I know condenser and oil maintenance are things that will keep your unit going.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  3. #3
    Join Date
    May 2011
    Location
    North FL.
    Posts
    180
    As far as I know, I don't think there is any 5 yrs tear down inspection. As long as you have been keeping good records on your oil analysis and providing proper annual maint. you should be good. May want to put that towards Eddie Current testing the tubes every five years, more frequent if water conditions warrant and or this is a critical unit. Give your question time and you'll have the correct answer

  4. #4
    Join Date
    Oct 2001
    Posts
    6,859
    punching of the condenser tubes..oil samples in the fall and or changes during winter maint work.check the electrical into the compressor terminals...megger readings ...tower wash down troth and straners cleaned.if you don't touch the tower(building does it) then maybe a midsummer condenser punch as an extra.location of the tower to the chiller will dictate new O rings for the heads if they are both on the same level what 50psi
    "when in doubt...jump it out" http://www.youtube.com/watch?v=Px5YcOeQB4I

  5. #5
    Join Date
    Oct 2001
    Posts
    6,859
    punching of the condenser tubes..oil samples in the fall and or changes during winter maint work.check the electrical into the compressor terminals...megger readings ...tower wash down troth and straners cleaned.if you don't touch the tower(building does it) then maybe a midsummer condenser punch as an extra.location of the tower to the chiller will dictate new O rings for the heads if they are both on the same level what 50psi
    "when in doubt...jump it out" http://www.youtube.com/watch?v=Px5YcOeQB4I

  6. #6
    Join Date
    Jan 2011
    Posts
    6
    All, thanks for helpful replies.

    The first vendor just worded “O-rings & gasket for reassembly” in proposal. The second vendor had also recommended EC & Tower cleaning – so based on responses, it sounds like they have a better understanding of the situation.

    I am guilty of launching a request that had the words “tear-down”. Before I went back to the first vendor to questions scope – I just wanted to get a little feedback, this site was very helpful on another chiller question I had. And I know the first vendor isn’t a hack – like the rest of us being busy, could have been a simple mix-up, but I wanted to get my ducks in a row before questioning their scope.

    thanks

  7. #7
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    When I hear "Tear down" I'm thinking "rebuild". But it it's just o rings and gaskets, then this might just man pulling the heads on heat exchangers, cleaning the tubes, inspecting the tubes sheets and probably do an eddy cureent test on the tubes to check for potential cracks. A 5 year interval probably isn't bad.

  8. #8
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992
    First off , don't think u will be brushing tubes on an 80 ton screw.,
    I'm thinking AIR COOLED,. As far as 5 year TEARDOWN, on a screw?
    Like said earlier, oil samples, clean cond coils., check with gages to manifold reading.
    But I am not dissing , is a good angle if they have $ to spend for routine gasket and ring change
    wait for alarms
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  9. #9
    Join Date
    Mar 2007
    Posts
    3,074
    What manufacturer and model chiller do you have? We may be able to give you a better idea of what needs to be done.
    "There is no greater inequality than the equal treatment of unequals."

    -Thomas Jefferson

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event