Results 1 to 7 of 7
    The Hot South
    Chiller Alarm Notification
    I have an account that is a retirement facility that has several chillers that run 24/7. Each building has one chiller and 1 chilled water loop. I'm looking for an inexpensive way to install a device on the alarm contacts on each chiller that will notify the front office or maintenance man when a chiller goes into alarm. They don't need a building automation system since each chiller runs 24/7 and its one chiller per loop/bldg.
    Any info will be much appreciated!
    Columbus Ohio
    I assume that you know most if not all chillers have a set of external alarm contacts.
    Wire up a relay circuit that will send an alarm to the desk, either light, audible, or both.
    Or are you looking for something wireless?
    UA LU189
    10mm, because it's better than .45acp
    The Hot South
    Quote Originally Posted by zw17 View Post
    Thanks for your reply.
    Yes I'm aware of the alarm contacts and I thought of the relay circuit but the complex is several buildings over 9 acres. It would be a major job to pull that much wire. I was thinking of something wireless or something that can send a text message to a cell phone or something like that.
    Columbus Ohio
    UA LU189
    Jul 2011
    East coast USA
    Quote Originally Posted by fxb80 View Post
    I have used this, works great. Depending on the alarm your looking for. I have also seen where some alarms like water-temp alarms was tied into the fire alarm system as trouble alarm. either way your notified.
    The Hot South
    Thanks for the info. I checked out both solutions and they're both good possibilities.