    Flame rectification circuit

    On a electronic ignition intermittent pilot ignition control is there any known methods of testing the flame sensor besides measuring amperage? Was curious if any techs had different tricks or techniques.

  2. #2
    Join Date
    Feb 2012
    Location
    san pedro ca.
    Posts
    362
    The only way to check the amperage on a flame sensor is to plug it into a wall socket, Don't do that.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,411
    Quote Originally Posted by sgagne199
    On a electronic ignition intermittent pilot ignition control is there any known methods of testing the flame sensor besides measuring amperage? Was curious if any techs had different tricks or techniques.
    Not that I'm aware of.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,911
    X2.

    Microamps, pulsating DC.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  5. #5
    Join Date
    Feb 2012
    Location
    Upstate SC
    Posts
    84
    Some of the newer controllers will do that for you. Other than that I agree with the other posts.

  6. #6
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    76
    Ok thats kinda what i figured thanks for the input

  7. #7
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    5,469
    You can find manufactuers that make test devices like Honeywell made for the 890's and Fenwall made. What brand of control is it?
    Tracers work both ways.

  8. #8
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    17,911
    Quote Originally Posted by jburchstead View Post
    Some of the newer controllers will do that for you. Other than that I agree with the other posts.
    True. Some will give you a voltage reading that is intended to mimic the microamp reading.

    BUT, the approach being take is the same, regardless of having a circuit do the work for you.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  9. #9
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,075
    Hey coilcleaner, that's the stupidest thing I have ever heard
    It might get loud!

  10. #10
    Join Date
    Jan 2002
    Posts
    247
    As mentioned above there are several types of flame simulators on the market depending on type something like this: http://cgproducts.johnsoncontrols.co...PDF/121835.PDF
    Two wire hook up, three wire f**k up.