Results 1 to 12 of 12
    Mar 2012
    LANCASTER,PA.
    Hmm BECKETT AQUASMART
    Is anyone else having issues with the Beckett aquasmart low water control,The company I work for brought in the factory rep. to give us a full detail when installing these controls and we are getting call backs for low water lock out,we try to re-set them but we wind up changing the probes.Some of the calls are going on a new 3rd sensor replacement?,Any feedback would be greatly appreciated,We talked to the rep. and he is unaware of any issues with these!!!
    Thanks!!!!!!!!!!!!!!
    Jan 2012
    Broomall, PA
    I wonder if it's a bonding/grounding issue? You put in the new correct length well, right? There is a difference between the "a" & the "b" model, as far as how the green wire is attached, so double check that.
    Mar 2012
    LANCASTER,PA.
    Thanks,I will check on this!
    pulaski ny
    are you using pipe dope or tape?
    Mar 2012
    LANCASTER,PA.
    tried both individually.
    pulaski ny
    are you guy's the only ones that have this problem? or is this a common issue? what does the rep have to say?
    Mar 2012
    LANCASTER,PA.
    Well the rep tells us he is not having anyone else with these issues?and he is looking into this?
    pulaski ny
    does he have you test the probes before they are condemmned? can you test them? i have never used these. i stick with guard dog. they seem to be the most reliable.
    pulaski ny
    Quote Originally Posted by STEVEusaPA View Post
    i have never used these, how do they work if they are in a well?
    Mar 2012
    LANCASTER,PA.
    He is having us return them to his office and he tells us he will follow up on this??
    Jan 2012
    Broomall, PA
    Reply to snup...
    Basically, attach grounding/bonding strap to boiler (return pipe). Probe sends low voltage thru probe, picked up by ground. When water level drops below probe level, breaks continuity. Good ground and bond are important, and the source of most problems. This is a better explanation.
    http://www.beckettcorp.com/protect2/...martmanual.pdf
    Mar 2012
    LANCASTER,PA.
    THANK YOU!!!
