    Is this normal. Ori and Cond. fan cycling
    Ori and condenser fan cycling on the 2nd fan of a two fan condensing unit.
    Keeprite M/n KH200H2-HT3#-1931.
    Wouldn't the ORI valve be enough?
    ENJOY THE RIDE
    Quote Originally Posted by Peztoy
    Yes, the ORI is enough, but many manufacturers cycle the second fan, too.
    Saves a bit if energy.
    I've seen it & even asked the same question once upon a time. here's the link
    http://hvac-talk.com/vbb/showthread....ght=headmaster
    Sent from my HTC Sensation 4G using Tapatalk
    Apr 2010
    Ontario
    Thanks guys. I'll leave well enough alone.
    ENJOY THE RIDE
    May 2011
    Chas.,WV
    By cycling the second fan you also reduce the amount of refrigerant required for low ambient operation.
    Quote Originally Posted by Ben Wulkin
    I doubt it
    Jan 2012
    ohio
    what is an ori valve ?
    Stongsville Oh
    Sporan Open on Rise at Inlet. Used in low ambient head pressure control headhttp://www.legacychillers.com/cms_data/uploads/Sporlan-90-30-floodedvalve.pdfhttp://http://www.legacychillers.com...oodedvalve.pdf pressure control.
    ckartson
    I didn't write the book I just read it!
    Quote Originally Posted by royd2 View Post
    Open on Rise of Inlet(ORI) ..
    Open on Rise of Inlet valve.
    It is a valve used to flood the condenser during low ambient conditions.
    http://sporlanonline.com/90-31.htm
    http://sporlanonline.com/90-30-1.htm
    A little light reading on the subject
    Jul 2001
    Gold Coast of Connecticut
    Many times the ORI has vever been set here. In Ct many stores have 100% fan cycling, but when the temperature drops even with all the fans off the ORI is needed to maintain minimum head pressures for the TXV's to feed. I have seen a rack stall when the head is lower than the Low side cut in setpoint with the ORI open all the way.
    Aire Serv of SW Connecticut- Gas heat, dual fuel and central a/c systems installed and serviced
    Quote Originally Posted by Freezeking2000
    Yep. I've seen that, too.
    Had a neat one not long ago with a case that couldn't keep temp.
    The ORI was set too low and I wasn't getting enough pressure drop across the TEV.
    Raised the ORI to an appropriate level and it took off and ran.
    Apr 2010
    Ontario
    When you say "a rack stalled". Does this refer to when the ori is holding back the refrigerant in the condenser and permitting very little to no refrigerant in the liquid line?
    ENJOY THE RIDE