    Answer the phone, we got a problem boss !

    One of my guys called today, pulled fuses, unit continues to run. I'm not sure what to think, so he sent this picture. I'll talk to him in the morning to see what he eventually found with it, unit got changed out anyway.

  2. #2
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    It's pretty obvious. The power doesn't go through those fuses. Either the fuses were bypassed in the disconnect, or that wasn't the disconnect for the unit.

  3. #3
    Join Date
    Feb 2012
    Location
    san pedro ca.
    Posts
    362
    Post Likes
    Or someone hard wired that sucker. Always check for voltage before touching wires. I have found several units like this.

  4. #4
    Join Date
    Apr 2007
    Location
    Saint Augustine, Florida, United States
    Posts
    1,248
    Post Likes
    you replaced a unit, interesting. hope you replaced the bypassed disconnect.

  5. #5
    Join Date
    May 2000
    Location
    Urbandale IA. USA
    Posts
    5,456
    Post Likes
    Perpetual motion !
    .
    Those who dance, appear insane to those who do not hear the music.
    Those who believe, appear ignorant to those who do not know God.

  6. #6
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,886
    Post Likes
    Lady next door called , her condenser stopped working.
    You need to put the phone down and get back to work!

  7. #7
    Join Date
    Apr 2007
    Location
    Tucson, Arizona
    Posts
    1,348
    Post Likes
    Thread Starter

    Kind of got an answer on this one

    The homeowner tied in a piece of equipment in the garage (behind disco), apparentlty the way he double lugged and hooked it up backfed 115v back thru the load side. The homeowner disconnected his contraption and everything worked normal but through my guys off. He was doing something with 3 phase equip. hooked with a 3rd leg generator. I still don't understand exactly what he was doing or why and how. I'll stop by on monday to check on everything and make sure he hasn't tied into our equipment again, maybe get a more thorough understanding.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by JWB View Post
    you replaced a unit, interesting. hope you replaced the bypassed disconnect.
    My thoughts exactly.

    It's broke, you need a new one.




  9. #9
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Quote Originally Posted by shavedneon View Post
    but through my guys off.
    through:
    [throo]
    preposition

    In at one end, side, or surface and out at the other: to pass through a tunnel; We drove through Denver without stopping. Sun came through the window.


    Threw:

    verb (used without object)
    to cast, fling, or hurl a missile or the like.

    noun
    an act or instance of throwing or casting; cast; fling.




    I would have done the same thing.
    UA LU189

  10. #10
    Join Date
    Feb 2007
    Location
    Central NJ
    Posts
    667
    Post Likes
    it's haunted. Obviously.......
    You have to pay your due's before you pay the rent!

  11. #11
    Join Date
    Aug 2008
    Location
    San Clemente, CA
    Posts
    1,424
    Post Likes
    We had one that we could not turn off the power too, even with the main c/b turned to off. We had to pull the meter and it was still on but that gave us the answer we were looking for, someone hooked it directly to the utility wires before the meter. Free a/c? It was a bank owned, got purchased and they were fixing it up to flip so we don't know who did it. Very dangerous being the wiring was not protected ether.

  12. #12
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    Quote Originally Posted by jnsrose View Post
    Lady next door called , her condenser stopped working.
    Lol ...

    Sent from my HTC Sensation 4G using Tapatalk

  13. #13
    Join Date
    Mar 2012
    Location
    Las Vegas, NV
    Posts
    17
    Post Likes

    Ohm's Law

    Remember that according to Ohm's Law that if voltage goes down, Amps go up. If your unit was rated at 230V and was only given 115V and running, the Amperage drawn was doubled. The motors and compressor were certainly not rated for that amp draw and the product was overheated. That heat would destroy your motors if it weren't for the thermal overloads inside the motors/compressors to protect them. Also remember anytime a safety is tripped, it is weakened. This means that you are lucky the safeties worked. But what the heck is going on around you? Your A/C is a huge liability and nobody should steal power from it's disconnect, as that is against any code. With less than a $40 breaker (most are less than $20) and the same wiring to the equipment, the same voltage can be utilized in a safe manner to the equipment/operator and the HVAC system can remain isolated on it's own circuit as it should always be.

  14. #14
    Join Date
    Jul 2002
    Location
    Chariton, Iowa
    Posts
    619
    Post Likes
    That's not Ohm's Law, that is a trait of constant wattage devices like induction motors driving a constant torque load, IE a compressor or conveyor belt, and SMPS (switched mode power supply) loads. For a compressor when you reduce the voltage the amps do go up until you hit a point where the motor can no longer supply the required torque and it stalls, at which point the amps go up to the locked rotor number till the overload device trips.

    For fans and blowers motor power is to the square of the RPM and torque is directly proportional to airflow so with the right style of induction motor if you reduce the voltage you reduce the speed also, this is how the speed taps on a PSC blower motor work, the high tap is the lowest voltage tap of an autotransformer built into the run winding, the low speed is the highest voltage tap, the autotransformer function just intentionally undervolts the motor to make it run slower under load. With no load a PSC fan motor will turn the same speed on all speed taps. Try it some time, with the motor on high measure the voltage from the low tap to neutral.

    Note that there are also true 2 speed induction motors for belt drive blowers that start and run as a 4 pole for high but start on 4 pole and switch to 6 pole for low.

    IOW a 230v PSC CFM or IDB motor will run on 115 volts, it will just turn slower. A 230V compressor may start on 115v but will stall as soon as pressure starts to build up.
    To get the degree symbol ° on Windows hold down the Alt key and type 0176 or 248 on the keyboard number pad. It is also available via the character map, and on Windows 8.1 devices with a touchscreen via the on screen keyboard.

    There is no "E" in either BluVac or Blu-ray Disc.

    If you are the type where the painting is more important than the frame, or you just like movies, join me in listening to the widescreen.org podcast.

  15. #15
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,846
    Post Likes
    That's one of them new Nester wireless units. Ties right into the local hotspot and away it goes!
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •