Thread: moisture in system.. this ? always sparks good conversation..

  1. #1
    Join Date
    Feb 2012
    Location
    PA
    Posts
    30
    Post Likes

    moisture in system.. this ? always sparks good conversation..

    Can anyone prove or disprove whether a system(especially containing POE oil) can collect moisture due to a positive pressure leak??

    Ex. Medium temp refrigeration system using R-22 w/ POE oil(pressures obviously never even get close to a vaccum) tests positive for high moisture in oil. System has many small leaks, but has never been opened up for a repair.. Im referring to the possibility of the oil in the system collecting moisture as it runs, not the possibility of some idiot throwing a gauge full of air on the system.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    I've heard of it, but am unable to offer concrete and documented proof of it.

    The concept is a poorly timed and located Venturi due to a leak. High velocity refrigerant creates a negative pressure zone that allows moisture into the system.

    I'm far more inclined to believe that there is another explanation.



  3. #3
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    I could see it happening but I am willing to bet you would pick up far more non condensables first and would see those issues long before you would see moisture problems.

    Unless the pipe was submerged.
    UA LU189

  4. #4
    Join Date
    May 2003
    Location
    Utah
    Posts
    921
    Post Likes
    Always possible that the moisture was present in the POE and introduced that way.....POE does, after all, have a love affair with water.

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by bunny
    Always possible that the moisture was present in the POE and introduced that way.....POE does, after all, have a love affair with water.
    Much more likely.

    Evacuation doesn't remove moisture from POE.

    You need driers to do that.



  6. #6
    Join Date
    Nov 2011
    Location
    British Columbia
    Posts
    48
    Post Likes
    No way. I wouldn't believe that even if the unit somehow ran under water.

    Moisture has a mass and it moves by force like everything else. Until the forces equalize, moisture will stay where most convenient.

  7. #7
    Join Date
    Feb 2012
    Location
    Alabama
    Posts
    386
    Post Likes
    Quote Originally Posted by RuralSpaceman View Post
    No way. I wouldn't believe that even if the unit somehow ran under water.

    Moisture has a mass and it moves by force like everything else. Until the forces equalize, moisture will stay where most convenient.
    Same thing I was thinking, but what do I know? Been doing resi all my life.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Do either of you understand Bernoulli's Principle?

    Also known as the "venturi effect"

    http://en.wikipedia.org/wiki/Bernoulli's_principle

    Study up.


    I believe that it is possible, but would be extremely difficult to document and prove.



  9. #9
    Join Date
    Nov 2011
    Location
    British Columbia
    Posts
    48
    Post Likes
    Yes I remember Bernoulli's Principle from my industrial gas fitter's course, but I'm not sure it applies in a case like this. I can't think of any part of a refrigeration system that would form a venturi effect sufficient to overcome the force of escaping gas.

  10. #10
    Join Date
    Jan 2012
    Location
    PAC-NOR
    Posts
    46
    Post Likes

    Talking

    Quote Originally Posted by jpsmith1cm View Post
    Do either of you understand Bernoulli's Principle?

    Also known as the "venturi effect"
    http://en.wikipedia.org/wiki/Bernoulli's_principle

    Study up
    I believe that it is possible, but would be extremely difficult to document and prove.
    Tranes without LPCOs and the "Green Slimer" when pressures get low. It does happen, in very specific circumstances. On resi gear, you can't place enough suction/LL dryers to clean that mess up. R11x and ERPing was trane's SOP during that rash.

  11. #11
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    1) Yes, a venturi can form and draw air with moisture into a system.

    2) Yes, the moisture can already be in the oil, unless it is carefully contained and kept from exposure to moisture before it is placed into the system. POE is extremely hygroscopic.

    3) Now, from what I have been told, a dryer cannot remove moisture from POE oil. In mineral oil, the moisture is merely entrained with the oil. In POE, the moisture bonds with the oil chemically, and that makes it virtually impossible for a passive dryer to remove it. At least, that's what I was told. I may be wrong.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    I was told that a drier is the only way to remove moisture from POE.

    You won't remove it with a vacuum pump, that's for sure.


    There are also issues with water causing chemical changes in POE oil and causing it to revert back to its component chemicals, namely acid and soap.

    Plugged cap tube, anyone?



  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    32,658
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I was told that a drier is the only way to remove moisture from POE.

    You won't remove it with a vacuum pump, that's for sure.


    There are also issues with water causing chemical changes in POE oil and causing it to revert back to its component chemicals, namely acid and soap.

    Plugged cap tube, anyone?

    It will be interesting to learn more about this. We have a very small number of RTU's that use POE, so this is not an issue for us right now. Maybe I'll try to research the dryer aspect some more when I have time.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  14. #14
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Bernoulli's Principle only applies if the velocity inside the pipe that has a small hole is so high that it starts drawing air into the hole and not letting any refrigerant out.

    Lets just take a low temp running R404a with a -15 evap temp, 20 psig, and a small hole in the suction pipe. The velocity would have to be extremely high to ever reverse the 20 psi gas leaving the pipe and start drawing in air.

    For a leak to leak gas out and suck gas in at the same time is completely impossible. You either have to take the pressure inside the pipe down to negative, or get the velocity so high it would create a slight vacuum at the leak(not gonna happen in a refrigeration system, velocity would never get that high). Maybe if you got the pressure down to .5psig you might have enough velocity to suck a little air in, maybe.

    Urban Legend.

    The more likely cause of getting moisture into a system would be having a leak in the low side and some intermittent restriction causing negative pressures at times, or a pump down system that is pulling down into a vacuum due to pressure switch set wrong.

  15. #15
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by chuckcrj
    Bernoulli's Principle only applies if the velocity inside the pipe that has a small hole is so high that it starts drawing air into the hole and not letting any refrigerant out.

    Lets just take a low temp running R404a with a -15 evap temp, 20 psig, and a small hole in the suction pipe. The velocity would have to be extremely high to ever reverse the 20 psi gas leaving the pipe and start drawing in air.

    For a leak to leak gas out and suck gas in at the same time is completely impossible. You either have to take the pressure inside the pipe down to negative, or get the velocity so high it would create a slight vacuum at the leak(not gonna happen in a refrigeration system, velocity would never get that high). Maybe if you got the pressure down to .5psig you might have enough velocity to suck a little air in, maybe.

    Urban Legend.

    The more likely cause of getting moisture into a system would be having a leak in the low side and some intermittent restriction causing negative pressures at times, or a pump down system that is pulling down into a vacuum due to pressure switch set wrong.
    We need the Mythbusters!!




  16. #16
    Join Date
    Nov 2010
    Location
    MN
    Posts
    147
    Post Likes
    Check out this video on YouTube of a guy pulling a vacuum on a clear bottle of POE that came out of a new scroll compressor. http://www.youtube.com/watch?v=NzXO8...e_gdata_player

  17. #17
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by PMARS2345
    Check out this video on YouTube of a guy pulling a vacuum on a clear bottle of POE that came out of a new scroll compressor. http://www.youtube.com/watch?v=NzXO8...e_gdata_player
    Means nothing.

    Yes, some moisture came out of the oil.


    After he's done, send that stuff out for an analysis and see what the moisture content is.

    You'll be in for a surprise.



  18. #18
    Join Date
    Nov 2010
    Location
    MN
    Posts
    147
    Post Likes
    Quite a few statements on Poe oil here, any references to back then up? I'm nottt doubting what is said would like more info for learning?

  19. #19
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    http://sporlanonline.com/November%20...Cold%20WAR.pdf

    There is a start.

    There are many, many threads here on this topic. Use the search feature.



  20. #20
    Join Date
    Nov 2010
    Location
    MN
    Posts
    147
    Post Likes
    Thanks

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •