I went to class on communicating heat pumps from trane and they try to sell me a self charge tool to plug in to the control board for 100.00 and i so I made my own myself with a solenoid valve and two spade,s and two taps same thing they are selling in a fancy black box,,
03-02-2012, 10:17 PM #2
- Jan 2012
- PAC-NOR
- 46
The infamous "Charge assist" crap. Pump to the ID, recover, weld in a REAL suction port, and charge by SH/SC. They made the ChargeAssist to be a hookup, run, unhook. Amb temps have to be... above 70 If I recall correctly, and we've sent back all CA boards. I'd suggest NOT posting any diags
03-03-2012, 06:33 AM #3
Professional Member*
- Jul 2006
- Virginia
- 3,713
just hook up your guages to the suction port push the button and and add refrigerant untill the led changes to charged then turn off the guage i always monitor the superheat and subcooling also ,as for the charge assist the boss *****ed to the tm untill he gave us 2 of them at no charge
03-03-2012, 08:40 AM #4
03-03-2012, 08:48 AM #5
03-03-2012, 10:58 AM #6
- Jul 2006
- Virginia
- 3,713
03-03-2012, 11:00 AM #7
I've done several of these, and you cannot charge in heat with the charge assist. Only in AC mode with ODA above 70 degrees.
03-03-2012, 12:58 PM #8
03-04-2012, 02:57 PM #9
on the XL20i you can use charge assist if ID temp is in the 70* range and outdoor temp is 55* and above.
03-04-2012, 03:13 PM #10
also these charge assist boards have pretty accurate transducers and thermistors. they are most likely way more accurate then your normal gauges.