    RTAA ice build complete

    I have an RTAA that when commanded to start ice build mode immediately goes to ice build complete. My entering and leaving temps are well above set point so it's not a sensor problem. HELP!

  2. #2
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    because they give more information?

  3. #3
    Join Date
    Jun 2005
    Location
    cocoa, fl
    Posts
    5
    Post Likes

    ?

    "because they give more information" what does that mean? Was your response cut off?

  4. #4
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    more information about the machine? temperatures? etc.

  5. #5
    Join Date
    Jun 2005
    Location
    cocoa, fl
    Posts
    5
    Post Likes
    EWT-37 DEG, LWT-34 DEG, ICE BLD COMPLETE 24 DEG. COMMAND CHILLER INTO ICE MODE, PRIMARY PUMPS COME ON, VALVES OPEN, CHILLER HAS NO ALARMS BUT DISPLAY GIVES CODE A101 ICE BLD COMPLETE. VERIFIED TEMP SENSORS, VOLTAGE FOR COMMAND, PUMPS, VALVES AND FRONT END STPT.

  6. #6
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    what is your set point? in what way this machine? auto, local or tracer?

  7. #7
    Join Date
    Jun 2005
    Location
    cocoa, fl
    Posts
    5
    Post Likes
    Ice termination set point is 24F. Supply & return glycol temps are in mid 30's F. Unit is in Local mode.

  8. #8
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    mode of the machine, change it to ice machine, check the configuration of the machine

  9. #9
    Join Date
    Feb 2010
    Location
    MEXICO
    Posts
    480
    Post Likes
    what's your email?

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,851
    Post Likes
    your contacts that INITIATE ice building are opening after they close. I would recommend that you investigate the BAS that is controlling this feature. take a jumper and...wait...investigate first.

    any diagnostics?
    Have you ever noticed that geese walk around like they are drunk and trying not to get a public intox ticket?

  11. #11
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,748
    Post Likes
    Quote Originally Posted by jayguy View Post
    your contacts that INITIATE ice building are opening after they close. I would recommend that you investigate the BAS that is controlling this feature. take a jumper and...wait...investigate first.

    any diagnostics?
    I was thinking the same thing.

  12. #12
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,562
    Post Likes
    He said in post #5 that "chiller has no alarms", but people unfamiliar with this panel have been known to get confused on how to check for current alarms and alarm history. Come to think of it, so have people who are (supposed to be) familiar with it.