    Quote Originally Posted by John Markl View Post
    If we restrict airflow, it stands to reason that we are rejecting less heat....So, wouldn't subcooling go down?

    If you have a dirty condenser, your head pressure is high, and your subcooling low...Washing the coil brings the head pressure down and the subcooling would rise, yes?
    Actually my experience has shown otherwise. If you raise the head pressure by restricting airflow you didn't change the entering air temp. The pressure goes up, but the refrigerant temp doesn't go up as much, resulting in higher SC. The approach temp (difference between entering air and leaving refrigerant) doesn't change much, but the head pressure went up.

    But if you raise the head pressure by raising the entering air temp, both temp and pressure will go up together resulting in the same SC.

    I will definitely be testing it this summer again to be certain.

  2. #42
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    I will definitely be testing it this summer again to be certain.
    You and me bof....

    I'm sitting here thinking......Systems with sight glasses that I work on, that have fan cycle controls......as the head pressure rises, just before the pressure switch cuts in, the glass loses liquid and turns to vapor, and the liquid line gets warmer....when the fan comes on, within seconds, the glass is back to liquid and cooler.

    Oh well, off to the theater....("Kurves")....catch ya later
    Technical incompetence is NOT a sales tool....

  3. #43
    Join Date
    Feb 2012
    Location
    VA
    Posts
    108
    Post Likes
    Remeber yor laws increas pressure increase the temp it should increase your SC

  4. #44
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by John Markl View Post
    You and me bof....

    I'm sitting here thinking......Systems with sight glasses that I work on, that have fan cycle controls......as the head pressure rises, just before the pressure switch cuts in, the glass loses liquid and turns to vapor, and the liquid line gets warmer....when the fan comes on, within seconds, the glass is back to liquid and cooler.

    Oh well, off to the theater....("Kurves")....catch ya later
    Its the opposite but I've seen it too
    These units with receiver and fan cycling need more charge than a unit with a head pressure control valve so you don't loose the liquid at the dip tube

    Also just because a sight glass isn't clear doesn't always mean there is no SC



    Bottom line was liquid temp where they intersect the glass flashed
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #45
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by chuckcrj View Post
    Actually my experience has shown otherwise. If you raise the head pressure by restricting airflow you didn't change the entering air temp. The pressure goes up, but the refrigerant temp doesn't go up as much, resulting in higher SC.
    Your observations are accurate. The explanation I've seen is low condenser air changes the "design" of the condenser coil, maybe suggesting it's about like removing a few rows of tubing, resulting in a smaller coil volume. The end result is a smaller coil with the same amount of refrigerant contained. The liquid would stack further back, increasing subcooling. I don't fully comprehend the reasoning, but it does sound good. And I can't come up with anything better.

  6. #46
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Post Likes
    I attended a class put on by Rheem tonight after work....They gave us a book, and Table 23 says that "Low Condenser Air Flow = High Discharge Press ure and Low Subcooling"
    Technical incompetence is NOT a sales tool....

  7. #47
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by John Markl View Post
    I attended a class put on by Rheem tonight after work....They gave us a book, and Table 23 says that "Low Condenser Air Flow = High Discharge Press ure and Low Subcooling"
    So, who do you believe?

  8. #48
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Post Likes
    Quote Originally Posted by Saturatedpsi View Post
    So, who do you believe?
    Obama....
    Technical incompetence is NOT a sales tool....

  9. #49
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Saw the Fieldpiece charging jacket in the RSES Journal so my measurements must be wrong.
    Maybe I should try it again with a set of analog gauges and pocket thermometer
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  10. #50
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    I wouldn't argue the point, were it not for the fact I've "staged" low condenser air numerous times, and it always resulted in increased subcooling.

    Quote Originally Posted by John Markl View Post
    If we restrict airflow, it stands to reason that we are rejecting less heat....So, wouldn't subcooling go down? Wouldn't the condenser have LESS liquid in the bottom 1/3 ?
    I believe the flaw in that reasoning lies in fact the condenser is rejecting essentially the same amount of heat. There is likely some decrease in net refrigeration due to elevated liquid temps, but whatever the amount of heat energy being taken in by the evaporating process, it is being rejected in the condenser. If it wasn’t, something would eventually blow up…

    The condensing process has adjusted for the reduced rate of heat transfer by generating a higher set of saturated conditions for condensing to take place. The same adjustment takes place as OD temps increase. But for reasons I don’t fully understand, reduced condenser air volume affects subcooling, where increased condenser air temperature doesn’t.

    To me, the intuitive conclusion is a relatively unchanged subcooling value in either case, assuming no change in the evaporator load.

    In the YouTube link, Jim Bergman discusses the “irregularities” of restricted condenser airflow, 12 minutes or so into the video.

    http://www.youtube.com/watch?v=SomBa...yer_embedded#!

  11. #51
    Join Date
    Dec 2011
    Location
    pensacola fl.
    Posts
    88
    Post Likes

    checking charge in low ambient

    Raising the head pressure should be enough. Its not necessary to have a load on the evap. For example, if you had a perfectly charged working unit except the RA fiter was dirty to the point that the coil started to ice over, in other words a no load condition. Would you expect this to make the subcool low? Raising head press and checking subcool should be enough, although I am willing to be schooled on the subject.

  12. #52
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by Saturatedpsi View Post
    I wouldn't argue the point, were it not for the fact I've "staged" low condenser air numerous times, and it always resulted in increased subcooling.



    I believe the flaw in that reasoning lies in fact the condenser is rejecting essentially the same amount of heat. There is likely some decrease in net refrigeration due to elevated liquid temps, but whatever the amount of heat energy being taken in by the evaporating process, it is being rejected in the condenser. If it wasn’t, something would eventually blow up…

    The condensing process has adjusted for the reduced rate of heat transfer by generating a higher set of saturated conditions for condensing to take place. The same adjustment takes place as OD temps increase. But for reasons I don’t fully understand, reduced condenser air volume affects subcooling, where increased condenser air temperature doesn’t.

    To me, the intuitive conclusion is a relatively unchanged subcooling value in either case, assuming no change in the evaporator load.

    In the YouTube link, Jim Bergman discusses the “irregularities” of restricted condenser airflow, 12 minutes or so into the video.

    http://www.youtube.com/watch?v=SomBa...yer_embedded#!
    Good video.

    It really illustrates the problem with checking or adjusting charge with restricted condenser airflow.

  13. #53
    Join Date
    Nov 2007
    Location
    Sherman, TX
    Posts
    9,441
    Post Likes
    We have customers that require year-round A/C.....which necessitates the use of fan cycling.

    It may be "irregular" but it works.
    Technical incompetence is NOT a sales tool....

  14. #54
    Join Date
    Nov 2011
    Location
    USA
    Posts
    4,451
    Post Likes
    Quote Originally Posted by bluecool View Post
    Raising the head pressure should be enough. Its not necessary to have a load on the evap. For example, if you had a perfectly charged working unit except the RA fiter was dirty to the point that the coil started to ice over, in other words a no load condition. Would you expect this to make the subcool low? Raising head press and checking subcool should be enough, although I am willing to be schooled on the subject.
    If the metering device is a TXV, the low evaporator load would result in the TXV closing down to maintain superheat which would create the same symptoms as a partial LL restriction, causing the subcooling to increase. If the head pressure is "artificially" raised by restricting condenser air, the subcooling would increase. Those results are reasonably predictable.

    If however, the metering device is fixed, I can only guess at what might happen. The low evaporator load will result in low suction and probably low superheat (depending on head pressure).

    If the head pressure is raised by restricting condenser air, the differential pressure across the orifice will increase, forcing more liquid through the orifice, probably reducing the amount of liquid in the condenser, which would lower the subcooling.

    But, I don't know what "normal" subcooling values are with fixed orifice systems. If airflow is design across both coils, the pressures are "normal", and indoor / outdoor temps are within operating ranges of the superheat chart, the system is charged to the specified superheat value and the subcooling is whatever it is.

  15. #55
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by John Markl View Post
    We have customers that require year-round A/C.....which necessitates the use of fan cycling.

    It may be "irregular" but it works.
    It certainly works, and works fine for low ambient cooling. I have Telecom buildings that cool by fan cycling down below zero.

    Just don't set the charge in low ambient by restricting airflow or you might be undercharged on a hot day.

  16. #56
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,815
    Post Likes
    I ordered one of these to test it out. I have posted one video and am uploading a second and maybe a third.

    http://youtu.be/pmFd8K-9hkU

    I tested it on a 13 seer R22 system in the shop, at about 68 degrees indoor air temp at the condenser and about 73 degrees RADB,
    JLB,

  17. #57
    Join Date
    Aug 2009
    Location
    Fort Lauderdale Fl
    Posts
    282
    Post Likes
    Is the main purpose restricting air flow? Seems like it's just short cycling a portion of condenser air. I only got a quick look at the hood at the beginning of the video

    Sent from my SPH-D710 using Tapatalk

  18. #58
    Join Date
    Jan 2005
    Location
    Akron
    Posts
    1,815
    Post Likes
    It actually just backs up the heat in the condenser. It is wrapped tight around the top so air does not recirculate.
    JLB,

  19. #59
    Join Date
    Nov 2008
    Location
    Northern California, foothills.
    Posts
    227
    Post Likes
    Quote Originally Posted by Saturatedpsi View Post
    If the metering device is a TXV, the low evaporator load would result in the TXV closing down to maintain superheat which would create the same symptoms as a partial LL restriction, causing the subcooling to increase. If the head pressure is "artificially" raised by restricting condenser air, the subcooling would increase. Those results are reasonably predictable.

    <snip>
    So if in low-ambient and low-evap conditions and
    trying to charge to the nameplate (TXV) subcooling value, the
    subcooling will change drastically depending on whether the
    condenser airflow is blocked off. (Right?)
    Say, for R410, what does one shoot for? A certain
    condenser pressure/temp range? (What might that be?)

    (Today, I weighed in a charge and blocked off the condenser
    such that condenser R410 sat temp got to about 84 degrees
    and subcooling was, I think, almost 20 degrees, a line temp
    of 64 F. Good thing I was weighing-in and not trying to shoot
    for a specific SC value, as I was a bit unsure what would have
    been correct under those conditions.)

    Thank you.

  20. #60
    Join Date
    Mar 2007
    Location
    On a bull named Foo Manchu
    Posts
    18,815
    Post Likes
    Quote Originally Posted by jim bergmann View Post
    I ordered one of these to test it out. I have posted one video and am uploading a second and maybe a third.

    http://youtu.be/pmFd8K-9hkU

    I tested it on a 13 seer R22 system in the shop, at about 68 degrees indoor air temp at the condenser and about 73 degrees RADB,
    Interesting Jim
    So that 13 seer unit calls for 10˚F SC
    The one I tested in this thread (multi speed high seer) calls for 16˚F SC and ran to spec with no air restriction @40˚F ODA.
    “If You Can Dodge A Wrench You Can Dodge A Ball”

+ Reply to Thread
Page 3 of 5 FirstFirst 12345 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •