Results 1 to 4 of 4
  1. #1
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,062
    Post Likes

    Re-Verber-Ray XTS Problem

    I am working on a Re-Verber-Ray XTS Radiant Tube heater.

    When I originally got the call, the location had 4 of 8 of theses heaters not working. 3 of them I was able to clean the intakes, blow out the section of the box with the gas valve, checked wiring, etc and they all fired right up.

    The fourth one, EVERYTHING was burnt up in it. The wiring, silicon control tubing, top of the gas valve, and the ignition control module.

    I rebuilt the unit, replacing everything but the blower and burner tube.

    The unit ran several hours.

    And it did it again.

    The Baffle seems intact, Blower running fine and is clean, flue clear. What would cause this blowback?

    I can't fix it if it won't stay broke..

  2. #2
    Join Date
    Sep 2006
    Location
    Ohio
    Posts
    664
    Post Likes
    The room could be in a negative pressure, the flue is getting a down draft or the combustion blower motor is going bad an not moving enough air.

  3. #3
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,062
    Post Likes
    Thread Starter
    I ended up talking to R-V-R today, and discovered this is a common problem in this particular installation, and it is due to neg pressure. It pulls the hot air back down the flue across all the plastics and wire and tubing and turns them to goo. Intake Has to be re-piped to outside the space or changed to the new XTS3 which is re-designed to correct this problem.

    So you are right.. and thank you.

    I can't fix it if it won't stay broke..

  4. #4
    Join Date
    Oct 2009
    Location
    new jersey
    Posts
    322
    Post Likes
    Liftcart or tall ladder on that?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.