    Leak Seal Repair

    How do you repair a perfectly good two door reach in refrigerator, that this stuff has been added to?
    Restaurant owner said that leak sealer had been added. The refrigerant (17oz.134a) had a sweet smell to it, and I don't know what brand or how much was put in.
    Found a restricted drier, replaced it. Now the cap tubes are stopped up.
    I don't want constant call backs on this unit due to restrictions or other malfuctions.

    I think I know what the fix is going to be, but would like to hear from someone who has faced this problem before.

  2. #2
    Join Date
    Apr 2007
    Location
    Scottsdale,AZ
    Posts
    80
    Where was the leak and is it still leaking? I personally wouldn't rely on that for a repair. Repair leak properly, flush system, change oil, replace cap tubes weigh in.new charge. Has compressor overheated?

  3. #3
    Join Date
    Aug 2010
    Location
    Galveston
    Posts
    9
    Not sure where the leak is. The thing iced over about 3 months ago. Thawed it out and it was working fine. (No auto defrost) Then yesterday no cool. I instructed owner to turn it off. When I got there compressor running a about 1 psi and the drier was frosting over. I am sure the compressor got hot running like that.

  4. #4
    Join Date
    Sep 2009
    Location
    Northeast
    Posts
    102
    drier frosting over sounds like moisture.

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777

  6. #6
    Join Date
    Sep 2009
    Location
    Northeast
    Posts
    102
    and keeping the condenser cleaned all the time.

  7. #7
    Join Date
    Jan 2010
    Posts
    6,382
    [QUOTE=GlenM;12569771] repair a perfectly good

    Sounds contradicting to me.

  8. #8
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    Quote Originally Posted by jpsmith1cm View Post
    Buy a new one?
    X2

    For you to properly repair this piece of equipment now that sealant has been added. it would cost more than a new unit.

  9. #9
    Join Date
    Aug 2010
    Location
    Galveston
    Posts
    9
    jp
    That was my thinking.
    The condensing unit is on top of the refrigerator as well as the evaporator, which is enclosed in an insulated box.
    I was preparing to remove cap tubes, remove copper from condensing coil, remove suction line and change compressor.
    Flush the coils. Then replace the copper, drier and cap tubes.
    However I still don't know if this going to work. The sealer may harden up before I can flush it out.

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,777
    Well, the other option that I've heard is to remove the cap tubes and blow straight air through the rest of the lines.

    Since these sealers harden when exposed to moisture, air will carry enough moisture to harden all of the sealant.

    Then you can change the oil, replace the cap tubes and evacuate and charge the system.

  11. #11
    Join Date
    Aug 2010
    Location
    Galveston
    Posts
    9
    Changing the oil on the compressor might be a better first option than changing compressor. If it does not gum up the valves. (Recip)

  12. #12
    Join Date
    Jul 2005
    Location
    Southern California
    Posts
    586
    I hear wedding bells...you might be married to this thing.
    Knowledge is knowing that a tomato is a fruit. Wisdom is knowing not to put it in a fruit salad.

  13. #13
    Join Date
    Aug 2010
    Location
    Galveston
    Posts
    9
    LOL
    Man, don't say that. I will have the refrigeration patrol on me.
    I already have ole KK (Koolant Kooler)

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event