    Intermittent open liquid sensor
    I have come across an intermittent open sensor alarm used on liquid level sensors for hussmann protocols. Not sure the make of the sensor off hand. I heard when the liquid stacks up to full or goes down to zero these sensors can just go into short sensor or open sensor scenerio.
    Ofcourse every time i'm there and graph it its reading and the graph history is normal. But doesn't the graphs log after every 3 min intervals, so if something would spike for a spilt few seconds it would not show on the graph anyways? ya know what i'm trying to say i hope.
    kinda lost right now or just to damn burned out to think
    I've had a few of the dials fail and do that.
    If you've got an E2, you can also tweak the minimum and maximum voltages before it gives an alarm.
    Nov 2005
    It is hooked up to a E2. I guess that's in the setup where you can adjust voltages? So this could solve the intermittent sensor fail alarm?
    Quote Originally Posted by -frozen-ocean-
    Yes.
    It is under the input setup.
    California
    I do this to all liquid level sensors. dial type or rod's.
    California
    This should assist you
    I also like to change Sensor type to Linear with PCT engineering units and Sensor units as V.
    It seems to track better than when set as "liquid level" or "refrig level"
    Sep 2006
    Good stuff!
    Jul 2005
    Southern California
    I've had a similar problem at a store. The min and max voltages were changed in the setup and the problems disappeared.
    Knowledge is knowing that a tomato is a fruit. Wisdom is knowing not to put it in a fruit salad.
    California
    other things to check too
    make sure it is wired correctly.
    make sure the input dip-switch is in the correct position.
    Nov 2005
    Thanks for the info :-)
    Dec 2006
    In a Mess
    this one is often overlooked in startups!
    Sig removed by mod. G-Rated site