    Orphaned water heater

    Hello. We are thinking of getting a new high-efficiency furnace, which would orphan the hot water heater. The terra-cotta heater flue has already been lined with 6" liner. If we orphan the water heater, do I need to put in a new, smaller liner (like a 3" liner)?

    Thanks!

  2. #2
    Join Date
    Jul 2009
    Location
    Columbia, MD
    Posts
    3,980
    not necessarily. you should find a company that is certified in combustion/carbon monoxide. a few tips. if you have a service guy hold a lighter up the the draft hood and say "yup its sucking the flame up" this does not mean the exhaust if flowing up the pipe. it means the room air is going up the pipe. for the most part you should be fine. but to be on the safe side i would have a barometric damper installed with a safety spill switch. and have some sort of low level CO monitor

  3. #3
    Join Date
    Jan 2006
    Location
    Powell River, BC, Canada
    Posts
    763
    There are vent sizing tables which need to be followed for proper appliance venting. You need to know the total chimney height, btu input of the appliance, vent connector height, horizontal run and number of elbows and the tables will give you the correct sizes. Make sure that the HWT is either in a large enough space to use room air for combustion & venting, or (preferred) there is a direct source of outside air sized correctly to provide the necessary air to the appliance. Have a pro come out and evaluate what you have and make the necessary changes.
    Where are you? Are you done yet? I got ONE more call for you.....

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,085
    A 6" limner is within teh allowable size for a water heater with a 3" draft hood.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,837
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!