    commercial duct smoke detectors

    Hello:
    I mainly work on commercial refrigeration(I.e. Supermarkets) but I was called out on fire alarm caused by an HVAC smoke detector. I found only one of five AHs with a tripped detector on the boiler sys. Removed cover and checked filters, screen and tubes on detector, all clean. The air filters were fairly new and the blower belt is external. Any ideas on what may have caused the detector to trip?

    Thanks

  2. #2
    Join Date
    Jul 2010
    Location
    Oak Creek,WI
    Posts
    12
    Is the ductwork tied into the make up air unit. I've seen in the past AHU tied into the make up air unit and the smoke from the exhaust fan back feeds and trips the detectors.

  3. #3
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,765

  4. #4
    Join Date
    Feb 2012
    Location
    New York City
    Posts
    106
    I found smoke getting in from a kitchen exhaust two blocks away. They were smoking meat (very tasty) but a condo building was getting "campfire smells" from their makeup air system. The smoke detector on that unit had actually been removed.

  5. #5
    Join Date
    Jun 2002
    Location
    south jersey
    Posts
    1,105
    Did you rule out a fire? LOL
    You need to put the phone down and get back to work!

  6. #6
    Join Date
    Feb 2012
    Location
    san pedro ca.
    Posts
    362
    dust?

  7. #7
    Join Date
    Jan 2012
    Posts
    42
    Had a no heat call on Friday. Found duct detector tripped. Caused of problem newly installed elect. reheat coil. The initial burn off caused it to trip.