Westinghouse/ Email PE centrifugal compressors
Fellow workers,
Anyone currently overhauling this brand and age of chiller, from what I know McQuay/ Daikin have basically re-badged them.
I have rebuild service instruction on PE compressors from way back, just curious to know if tolerances etc have changed, would parts be readily available????
Any input helpful.
-
-
Post Likes - 1 Likes, 0 Dislikes
-
some of the tolerances has changed, some due to updates on parts, your original wheel will not fit the new high speed shaft and vice versa. Most high speed parts is not available so you would need to replace the entire high speed assy. New high speed assy would mean a new wheel. Low speed shaft seal has changed. Oil pump is different. Some McQuay offices will have some of the parts on the shelf that is no longer made.
-
Post Likes - 1 Likes, 0 Dislikes
-
Thanks for response.
Thought parts would be a problem, especially vintage chiller I'm looking at.
Whats your opinion on Turbocor compressor chillers???
l
-
As of right now only McQuay is using those compressors, as of the major manufacturers. Two lesser known manufacturers, Artic Cool and Smardt, are using them on their entire lines. I believe Artic Cool has an up-and-under series, that fits completely in thru a standard doorway. No knockdown required.
-
the mcquay wmc chiller that uses the turbocor compressors the customers loves them. I have had good luck with them. I have less problems with these than any other type.
-
Originally Posted by
freonrick
the mcquay wmc chiller that uses the turbocor compressors the customers loves them. I have had good luck with them. I have less problems with these than any other type.
You haven't had any warranty issues with those chillers? What does the annual service consist of since the compressor's oil-less?
-
I second that great machines
-
as far as warranty issues that I have had has been software problems or a system problem. for best operation let the turbocor control the tower water when posible. overall you may have a sensor go bad or a board go out. pm on the chiller same as any minus oil related work. there has been problems with check valves on the chiller not the compressor.
-
Post Likes - 1 Likes, 0 Dislikes
-
oem mcquay turbocor seems great!
retrofit not so good!
true knowledge exists in knowing that you know nothing.
-
McQuay offers a retrofit in a Turbocor? Smardt makes a chiller up to 800TR, two circuit w/tandem compressors. Artic Cool makes a chiller up to 1200TR, I believe it's two circuit w/trio compressors.
-
we are a turbocor dealer.
we do retrofits on old 5h, 6l, trane E, screws and wheels!
r-12,r-22 and 134a.
the r22 retrofits did not go that well
the 134a been better.
Originally Posted by
MechanicallyInclined
McQuay offers a retrofit in a Turbocor? Smardt makes a chiller up to 800TR, two circuit w/tandem compressors. Artic Cool makes a chiller up to 1200TR, I believe it's two circuit w/trio compressors.
true knowledge exists in knowing that you know nothing.
-
What is the largest HP compressor available? What refrigerants can be used? Can you retrofit a R11 or R 123 chiller?
-
125 tons
134-a mainly.
I think?? you can retrofit an r11 chiller ofcourse all you use is the evaporator and condenser!
everything else goes!
i guess if you did an r11 chiller you would also change the refrigerant to 134a?
water cooled stuff is best but i have heard of guys doing air cooled stuff, just not me!
Originally Posted by
MechanicallyInclined
What is the largest HP compressor available? What refrigerants can be used? Can you retrofit a R11 or R 123 chiller?
true knowledge exists in knowing that you know nothing.
-
I have stated this before. If you keep installing these compressors, we will all become parts changers. You do not rebuild this kind of cheap compressor. You replace it! So here we go, lets race to the bottom of our carreers. When you take away the skill that is required to work on these compressors, we will be replaced by cheaper unskilled hands. This is just my opinion. Take it as you will.
-
Post Likes - 2 Likes, 0 Dislikes
-
Originally Posted by
supertek65
125 tons
134-a mainly.
I think?? you can retrofit an r11 chiller ofcourse all you use is the evaporator and condenser!
everything else goes!
i guess if you did an r11 chiller you would also change the refrigerant to 134a?
water cooled stuff is best but i have heard of guys doing air cooled stuff, just not me!
McQuay's WMC goes to 400 tons with two compressors so the tonnage will probably will be a little less than 200 tons per compressor. The evap and condenser on low pressure machines has not been certified or stamped to handle any pressure over 15lbs, at least of all the ones I have worked on.
-
Post Likes - 1 Likes, 0 Dislikes
-
No one has had issues with IGBT, soft start or PWM modules???
-
only problem I've ever had was when they cycled to much and had to realign the shaft and bearings
-
On air cooled it's to hard to get all the oil out of the system when you retrofit.
-
If you still have overhaul manuals, could use copy of them. Have unit with ce 050 compressor r12. Need to do overhaul. Did not think anymore out their this old. Thanks