    Trane cvhe 800 , 460 volt.

    Looking for solutions, I have a chiller that trips chiller breaker on starter when transitions through generator test at a hospital, generator is sized for chiller. Its a ch530 platform. Chiller runs good and no motor issues. Breaker settings have been adjusted to manufacture recommendations. Any suggestions???


    Sent from my iPhone using Tapatalk

  2. #2
    Join Date
    May 2008
    Location
    Central Pennsylvania
    Posts
    630
    Post Likes
    What type of starter is on the machine? I take it that the main circuit breaker for the chiller is tripping...not just a fault through CH530?


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    320
    Post Likes
    Thread Starter
    Cutler hammer


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    320
    Post Likes
    Thread Starter
    Yes chiller breaker not building main


    Sent from my iPhone using Tapatalk

  5. #5
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    1,915
    Post Likes
    Have you watched the contactors and how they sequence during gen test.
    Federal Reserve, stealing your kids futures since 1913

    UA290

  6. #6
    Join Date
    Jul 2003
    Location
    Texas
    Posts
    320
    Post Likes
    Thread Starter
    Not yet I need to dig in a little more hospital not to accommodating


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    1,915
    Post Likes
    You might try to change it to an open transition and see what happens. I would love to get to troubleshoot this, I suspect a drop in voltage during transition, time to sell a soft start.
    Federal Reserve, stealing your kids futures since 1913

    UA290

  8. Likes manny238, ruuufuhbock liked this post
  9. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,937
    Post Likes
    Quote Originally Posted by chillerguru View Post
    ...generator is sized for chiller....
    I would be lying if I said that this didn't bother me. How was it "sized"? If it is sized just for the chiller RLA then the voltage regulator probably isn't big enough to handle the large transition spike.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  10. Likes stanbyyourword, CHILLERSVCMAN liked this post
  11. #9
    Join Date
    Jan 2010
    Posts
    12,748
    Post Likes
    [QUOTE=chillerguru;24396011 generator is sized for chiller. [/QUOTE]

    Does that mean the additional load of the chiller or just the chiller by itself ?

  12. #10
    Join Date
    Nov 2008
    Posts
    380
    Post Likes
    jayguy who you working for now

  13. #11
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    5,937
    Post Likes
    Quote Originally Posted by triggerhappy View Post
    jayguy who you working for now
    JCI...same work, different hat.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  14. #12
    Join Date
    Jan 2010
    Posts
    12,748
    Post Likes
    Good friend was with JCI but they sold out to CBRE so he's there now. Oversees the AT&T account. Boy did I get an eye opener when I walked thru one of those buildings.