    Quote Originally Posted by TwincamDave View Post
    10 KW is NOT 10 KW as a blanket statment. It is dependent on your line voltage to the heat strips. If one system has 248 v a/c and the other has 218v a/c they will put out different amounts of heat if all else is equal. Sounds more like a return air leak(pulling in cold attic air causing it to drop the temp coming out a vent) if the voltages are the same.
    I believe the 10 KW is 10KW statement was made in reference to it mattering that the old unit had a 70 amp breaker and the new unit has a 60 amp breaker.

    And since both units being talked about, were in the same house, the voltage is the same.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  2. #15
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    5,086
    Difference in airflow.
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #16
    Join Date
    Jan 2009
    Location
    Central Iowa
    Posts
    213
    Quote Originally Posted by TwincamDave View Post
    10 KW is NOT 10 KW as a blanket statment. It is dependent on your line voltage to the heat strips. If one system has 248 v a/c and the other has 218v a/c they will put out different amounts of heat if all else is equal. Sounds more like a return air leak(pulling in cold attic air causing it to drop the temp coming out a vent) if the voltages are the same.
    Huh?
    Sorry Dave 10KW IS 10 KW no matter what. P=I*E E=I*R Basic Ohm's Law. Does amperage change as voltage does? Of course..., look at the formula.
    Can two 10KW heaters put out different temperatures? OF course! But they still draw 10KW. Put 10KW through a heater wire and 10KW through a wet string and see which one lets off the most heat and you will see the difference.
    10,000 watts, no matter what numbers you use for voltage and amperage, as long as they multiply together and equal 10,000, is still 10 KW!

  4. #17
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,717
    Some 10 kw heaters are 9.6 kw some are 10.0 but the main difference is airflow

  5. #18
    Join Date
    May 2008
    Location
    Central Fla.
    Posts
    311
    Quote Originally Posted by blabath View Post
    Huh?
    Sorry Dave 10KW IS 10 KW no matter what. P=I*E E=I*R Basic Ohm's Law. Does amperage change as voltage does? Of course..., look at the formula.
    Can two 10KW heaters put out different temperatures? OF course! But they still draw 10KW. Put 10KW through a heater wire and 10KW through a wet string and see which one lets off the most heat and you will see the difference.
    10,000 watts, no matter what numbers you use for voltage and amperage, as long as they multiply together and equal 10,000, is still 10 KW!
    Sorry old man but if you take a 10KW heater at 240v. and then put 208v, to the same heater you will get approx 75% of the heat you did at 240v.
    41.6 amps with 240volts will produces 34,095 BTU of heat and the same heater with 208volt will draw 36.2amps and produce 25,713 BTUs of heat. You can't use Ohms law to calculate amps into btu's. but you can calculate amps x volts to get your wattage after that you have to multiply your watts by 3.415 to get your btu's. And the last time I checked 34,000 was hotter than 25,000.

  6. #19
    Join Date
    May 2008
    Location
    Missouri
    Posts
    3,565
    Really stupid question......Does it still heat the house OK? Or is one unit not heating it's area? Why the reason for the outlet temp. question?

  7. #20
    Join Date
    May 2008
    Location
    Central Fla.
    Posts
    311
    It depends on what the loads call for BTU wise. If it says you need 32,000 BTU's and you only get 25,000 BTU's then no. You really need to know what your voltage is and the heater rating. Again as I said before it's probly a duct leak on the return side pulling in cool attic air and dilluting the heat being generated.

  8. #21
    Join Date
    Dec 2011
    Location
    PA
    Posts
    98
    Quote Originally Posted by TwincamDave View Post
    Sorry old man but if you take a 10KW heater at 240v. and then put 208v, to the same heater you will get approx 75% of the heat you did at 240v.
    41.6 amps with 240volts will produces 34,095 BTU of heat and the same heater with 208volt will draw 36.2amps and produce 25,713 BTUs of heat. You can't use Ohms law to calculate amps into btu's. but you can calculate amps x volts to get your wattage after that you have to multiply your watts by 3.415 to get your btu's. And the last time I checked 34,000 was hotter than 25,000.
    I second this.

    Quote Originally Posted by TwincamDave View Post
    It depends on what the loads call for BTU wise. If it says you need 32,000 BTU's and you only get 25,000 BTU's then no. You really need to know what your voltage is and the heater rating. Again as I said before it's probly a duct leak on the return side pulling in cool attic air and dilluting the heat being generated.
    This would be a good start. Also checking the blower wheels to see if they are not dirty. One other thing would be considering the difference in years there might be a smaller ton blower drive in one vs. the other... I would need model numbers from both units to tell.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event