    Quote Originally Posted by smhardison View Post
    Is there a replacement for the obsolete Barber Colman TP 8101 three wire
    (red,yellow and blue) controllers.

    Thanks,
    Sam
    A word of caution - the Barber-Colman system used a controller output voltage of 0-15 VDC. Today's industry "standard" is 0-10 VDC. Hence, finding a replacement with 0-15 VDC is "almost" impossible.
    Now, if you are driving a Barber-Colman controllED device requiring a 6-9 VDC signal such as an MP-52xx. Honeywell has a TB6980 and a TB7980 with a 0-10 VDC output (dual or single ramp). These require 24 VAC to operate. Match the output polarity of the Honeywell with the Barber-Colman.
    If you have an application requiring an input signal beyond the 10 VDC, take a look at KELE.com. Examine a Kele DT13E signal conditioner.l
    If you are using a Barber-Colman staging relay, examine the Kele UCS-221 and UCS-421.

  5. #18
    Join Date
    Jun 2006
    Posts
    128

    TP-8101

    Ask your customer if he is using a 40 year old PC and he might understand what you're dealing with.

  6. #19
    Join Date
    Jun 2010
    Location
    Miami
    Posts
    257
    Hey, I have barber coleman vacuum tube stuff still on-line. The system 8000 is my "new" stuff. Sad but true

  7. #20
    Join Date
    Dec 2008
    Posts
    6

    Barber Colman MP-52xx

    I want to change a TP8101 out with a 0-10VDC output thermostat to control a Barber Colman MP-5200 series actuator. The data sheet for the actuator says the following:
    Compatible with: 2 to 15 Vdc from TAC System 8000,TAC NETWORK 8000, or TAC DMS controllers.
    Operating Span, Nominally 3 Vdc fixed. 4.5 to 12 Vdc are required to assure full stroke travel under various loading conditions.
    Nominal Extended Start Point, Approximately 6 Vdc.
    I saw a previous post on here where it said that that the actuator actually only needs a 6-9VDC signal to operate. Is this true?

  8. #21
    Join Date
    Jun 2010
    Location
    Miami
    Posts
    257
    Scott, you have little choice. Try a 0-10VDC controller and see how it works for you. The only other option is to replace the MP5200 actuator. In any case you still need a 24 volt transformer and a 0-10VDC controller.

    The MP5200 costs more than new 0-10vdc actuators and I have to wonder how much longer we will be able to buy them.

  9. #22
    Join Date
    Dec 2008
    Posts
    6
    Thanks for the response Russ. I am going to give it a try.

  10. #23
    Try a CTE-5202 analog electronic thermostat by KMC Controls. It can be configured as a replacement for a Barber Colman TP-8101, TP-8102, TP-8103, TP-8124, or TP-8125 and has a digital display and pushbutton setpoint adjust. An extensive applications guide can be downloaded from the KMC web site (http://www.kmccontrols.com/products/...artid=CTE-5202).

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event