    Melbourne, Australia
    Carrier 30RA HP fault
    Hi Everyone,
    Have a 30RA with the pro-dialog controller. Circ B continuously tripping on HP Fault #33 without even starting. Checked over pressure readings, manual HP switch not tripped 24v all ok. Even tried swapping transducers and hp switch onto circ A. Still circ B HP fault. Tested the two speed condenser fan, all ok. Would this possibly be a board problem? I have the Service Tool V program, will return tomorrow and connect up and check out again. Is there anything specific I should look for? Any info would be greatly appreciated. CHEERS.
    East of big city prices.
    30RAN or RAP?
    Ok after reading this thing awake did you happen to check the overload on the compressor starter? Motor temp switch?
    Hi TGL,
    The full model No is: 30RA 120A 0232-PEE
    I checked over the compressor contactors and overloads today, all o.k. Spoke with a Carrier Tech and he told me it will be a faulty board for that circuit.
    Had a suspicion that's what it would be. Now to replace the board, I have to call in Carrier to program the new one!! Thanks for your help, will let you know if new board fixes problem.
    Quote Originally Posted by chill bill View Post
    Hi TGL,
    Yep sounds like a different animal than we have over here.