Heat Pump
Hello All,
I wouyld kindly ask for your opinion. Just to double check the following...
Water to water heat pump operates in heating mode. If heating source temperature is increased, more heat can be extraxted and consequently COP is increased. Do you agree?
The same applies in cooling mode i.e. lower the heat sink temperature , EER is higher?
Thanks
-
02-17-2012, 10:33 PM #2
Professional Member*
- Join Date
- Nov 2001
- Location
- east kansas
- Posts
- 7,969
http://www.waterfurnace.com/literatu...n/SC1007WN.pdf
Yes, page 31 and 32 will give you the data you are looking for.Beware of advice given by some guy on the Internet.
-
02-18-2012, 10:31 PM #3
Regular Guest
- Join Date
- Jul 2010
- Posts
- 42
Yes that would be true. But how would you do that?
-
12-08-2012, 12:28 AM #4
New Guest
- Join Date
- Dec 2012
- Location
- London
- Posts
- 3
Yes and a heat pump basically works like air conditioning in reverse
-
01-01-2013, 12:23 AM #5
New Guest
- Join Date
- May 2012
- Location
- Washington
- Posts
- 2
Yes I agree because you will get a greater heat transfer due to the higher delta T, with presumably no change in the work input to the system.
-