Thread: trane chiller question
-
02-16-2012, 07:26 PM #14
Regular Guest
- Join Date
- Feb 2012
- Posts
- 9
sorry but i don't follow please tell me more i'm willing to learn if your willing to teach
-
02-16-2012, 07:47 PM #15
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 127
That diagnostic is usually caused by no flow through the barrel. Throttle the leaving water butterfly valve, if so equiped to see if you hear water flow. If it doesn't get really turbulant sounding, you don't have flow. Put gauges on to check for pressure drop to see if you have flow.
-
02-16-2012, 08:18 PM #16
Regular Guest
- Join Date
- Feb 2012
- Posts
- 9
thanks will do
-
02-24-2012, 08:01 AM #17
Regular Guest
- Join Date
- Jan 2012
- Location
- Perth Down Under
- Posts
- 26
A lot of Trane screw machines have a built in freeze protection where if the entering water temperature of the evaporator is cooler than the leaving and the chiller is enabled it will fail.
In my country, if this occurs it is because the chiller, controls the pumps and the enable signal is given to the chiller. When the pumps are started the protection is enabled and if there is a cool pocket of evaporator water in the circuit and the reversed temperatures occur the unit faults. To prevent this from occurring, start the chilled water pump at least 5 minutes before the chiller is enabled. Circulating the water evens out the temperatures in the circuit and since the chiller is not enabled, the protection is not active and the fault will not occur.
-
04-18-2012, 02:01 PM #18
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
Take time to think through the problem at hand, don't rush.
Similar issue just the other day. Except w/a hi ent water temp
Fault. Techn. Is new to chiller work, chiller started w/a hot loop.
Piping not well insul. Sun baked, water at 88.7' intake, so it shut
Off. So I told him call BAS to open valve and try in 20m.
Stable at 64',go ahead &start chiller & log readings. This was
After him starting & resetting sev. Times. Explained to him what
Occurred and advised for him to repeat where necessary.
-
04-18-2012, 02:04 PM #19
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
Completely Agree with gear drive guru. Same principle :
Differing applications.
-
04-19-2012, 06:48 AM #20
ent and leave water sensors reversed?
they are the same sensors, dont think this would be a problem
i was taught if someone ever replaces a sensor that it is best to run the wire all the way back to the board,
i am under the understanding if one cuts a sensor that it changes the resistance,
now, i ran across something the other day.,.,
was working on a RTAA1404 , going off on water temp, i changed the temp sensors in the ent and leave wells in the water lines at the machine., theses sensors tied in to the 695, come to find out i replaced the wrong one., i was supposed to change the water temp sensors on the barrol,.
question, why sensors on the cooler barrol,.(because factory mount safetys i would think) and external water temp sensors, in the water lines, more safetys?Last edited by milkyway; 04-19-2012 at 07:04 AM.
no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
04-19-2012, 09:28 PM #21
If it's an RTAC, the entering water temp sensor can be bound as the leaving water temp sensor and vice versa. If it's an RTAA, it's easy to switch them up at the plug on the chiller module.
I had an after hours call recently where the customer had pulled all of the wires out of the MTA plugs to clean the connections. When he put them all back, he got the saturated evap temp. sensor and suction temp. sensor for one of the circuits mixed up. The circuit would pump itself down into a vacuum. Being an RTAA170, it did not have a low pressure switch. I think it would eventually fail on high pressure or low superheat, can't remember which... Probably lucky the compressor didn't lock up.Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
04-19-2012, 10:06 PM #22
I am the best chiller mechanic that has ever graced this board with his presence and many if not all of the top chiller mechanics here crave my advice even though I rarely hand it out willy nilly.
that being said I will offer you a bit of advice for this chiller, please take heed....
sell the customer a new chiller, double the size and this will remedy all of you issues, i promise. The rest of you can continue with your day, thank you.Saving the world...one service call at a time.
-
04-20-2012, 12:01 AM #23
-
04-20-2012, 09:08 AM #24
-
04-20-2012, 11:00 AM #25
nm
-
04-21-2012, 08:06 AM #26
If it's an RTAC, the entering water temp sensor can be bound as the leaving water temp sensor and vice versa. If it's an RTAA, it's easy to switch them up at the plug on the chiller module
Ah ,.!no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!