TOTAL HR AIR COOLED CHILLERS
hello
does some one know about EWT to heat recovery heat exchangers using R-134a?
in a project i deal with the chileer IOM say that the min enetring water temp is 28C.
and that a BYPASSS VALAVE is needed.
can someone give some more info ?
rgrds
rony
-
04-15-2012, 05:47 AM #2
Moved to chiller forum.
-
04-15-2012, 09:38 AM #3
There should be a (bypass) with a balance valve between the supply and return water., the reasoning behind this is to balance the system.,
balance can mean, as for water pressure/flow and the other more advance reason could be to (control ) water temps.,no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
04-17-2012, 11:08 AM #4
Regular Guest
- Join Date
- Oct 2010
- Location
- GREECE
- Posts
- 20
Hi,
Most probably you have W/C and A/C condenser in series and the W/C (HR) condenser is a PHE and first in the line.
IOM indicates this because when the compressor is not in operation and water temp is below 28C then saturation of refrigerant may occur and fill up the PHE with liquid.
When compressor starts you may have hydraulic hammering and brake PHE.
The configuration may be pump – PHE – 3way and pump or loads in order to raise the temperature as quick as possible.
Hope my approach is helpful.
Regard,
CV
-
04-21-2012, 07:37 AM #5
New Guest
- Join Date
- Apr 2012
- Posts
- 3
?! hydraulic hammering
hi
asuume the unit is in the first comision and water temp is 20c.
the heat recovery water pump is "off" .
do you think in this situation we can face the hydraulic hammering ?
if the situation is like this how can the unit start up ?
we dont have heat source to heat the HR water at firs start !!!
to brake PHE at first start sound to me not so good !!!!
rony
-
04-21-2012, 08:37 AM #6
This is NOT a Do It Yourself site.
We get paid to solve these problems.
Some of you pro members needs to learn this. Keep helping for nothing and this site will be overrun with people asking you to use your knowledge for free.UA LU189
10mm, because it's better than .45acp
-
04-22-2012, 01:43 AM #7
New Guest
- Join Date
- Apr 2012
- Posts
- 3
hello ZW17
you are correct .
its my mistake to ask this question .
rony
-
04-22-2012, 06:33 AM #8


Reply With Quote