    CGAE pumpdown timer fault

    CGAEC404, ser# J96M84073. circuit 2 frequently violates the pumpdown timeout circuit safety. never can catch it doing it and have changed out the LP switch thinking it was hanging up. Still happens and am about to change the liquid line solenoid valve out. anyone deal with this issue before?


    r404a

  2. #2
    Join Date
    Jan 2012
    Location
    Perth Down Under
    Posts
    26
    Post Likes
    Just so that we are talking about the same machine is the CGAE a 2 circuit, reciprocating air cooled chiller with up to 2 comps per circuit? If so has it a RCM control module?

  3. #3
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    Thread Starter
    gear drive,
    two scrolls per circuit


    r404a

  4. #4
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    just so that we are talking about the same thing...

    While in pumpdown mode, the Low Pressure Cutout (LPC) did not open in 30 seconds so Compressor A was shut down anyway. LPC may be defective, LL solenoid valve either leaks or is not closing.

    this diagnostic?
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  5. #5
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    Thread Starter
    Thats it Jay. i am leaning toward solenoid valve intermittingly leaking by. I think I will change it out. thanks for the replies


    r404a

  6. #6
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    don't rule out a bad low pressure switch (or somebody is 'monitoring' it), solenoid valves that have been moved and they are farther away than normal, solenoid valves that have someone else controlling them (bad, bad BAS technician!), low to very low suction superheat or high head pressure possibly due to overcharge, non-condensibles, etc.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  7. #7
    Join Date
    Oct 2003
    Location
    tidewater, va
    Posts
    2,205
    Post Likes
    Thread Starter
    thanks for the input jay


    r404a

  8. #8
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    oh! and i thought of another thing last night...perhaps you have a compressor that is not pumping very well, especially at high pressure differentials.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •