Results 1 to 9 of 9
    tidewater, va
    RTAA 70 ton refrigerant storage to low side
    Serial number U96A32142
    Any chance I can migrate and recover over isolate and store charge in lowside (58 pounds) to change out a saturated condenser temp sensor?
    r404a
    Dec 2009
    Southern US
    Never have tried it, I've always pulled the charge and used the oppurtunity to weigh the charge! Be interested to see if anyone says it possible!
    I'm good at making things cold...You can ask my first two wives!
    Dec 2008
    Dixiana, AL
    Quote Originally Posted by r404a View Post
    r404a
    Absolutely, assuming the service valves hold.
    Ohio
    I have done it on the 100 ton compressors. No problems.
    tidewater, va
    thanks for the replies
    r404a
    Feb 2012
    EVERYWHERE
    You can if you run the other circuit so the evap is cold.
    Dec 2003
    45th Parallel
    I've done it also. When you start it up, pull the load solenoid wire and run unloaded for 5-10 min. Shouldn't have any problems.
    “If your work speaks for itself, don't interrupt.” ~Henry J. Kaiser
    MEXICO
    if you can change the sensor without removing the saturated condenser r-22, there is indeed a respect SB
    If you have two chillers, and the loop is colder than the outside ambient temp. you can run chilled water through the chiller you are going to repair and that will migrate most of the liquid into the evaporator, but you have to manually open the EXV first. The alternative is to run the other circuit to get the evaporator cold. Either way, you will have to open the EXV, migrate the liquid, close the liquid and suction service valves, and vapor recover down to a couple PSI.
    If the valves hold, you should be outta there in a few hours.
    The key to happiness is lower expectations.
    Don't pick the fly crap out of the pepper.