TRANE RTHC retrofit
Hello all,
On a flooded RTHC I want to rebuilt the electrical panel.
Do you know if there is retrofit kit to use CH530 instead of UCP2?
Thank you and best regards,
CV
-
02-15-2012, 04:08 PM #2
Professional Member
- Join Date
- Mar 2004
- Location
- Windsor ON Canada
- Posts
- 391
Try Micro Control Systems in Ft. Myers Florida. They can provide a controller to replace the UCP2.
-
02-15-2012, 04:19 PM #3
Professional Member
- Join Date
- Sep 2008
- Location
- A land down under
- Posts
- 285
The UCP2 platform has not been superseded for aftermarket so I do not believe a retrofit kit is currently available for RTHC to CH530, however there is no reason the parts could not be individually selected and installed as a field engineered retrofit. IMHO
Necessity is the mother of invention
-
02-17-2012, 07:18 PM #4
Regular Guest
- Join Date
- Jan 2012
- Location
- Perth Down Under
- Posts
- 26
If you can find a flooded RTHC chiller please let Trane know"............ Cause they never built one. The RTHC was the first falling film chiller built by Trane and has the external economizer on it.
I have never seen a replacement controller for these but what are the benefits to warrant the expense
-
02-17-2012, 07:49 PM #5
I don't know why you would need to do this, but if you really wanted to, you could piece the control panel parts together. You would also need at least 1 new EXV, and a new liquid level sensor. I don't think there is any way around that.
Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.
"It's called the american dream because you have to be asleep to believe it" -George Carlin
"A nation of sheep begets a government of wolves" -Edward R. Murrow
"I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney
Buy american made goods & support locally owned businesses!
-
02-21-2012, 12:33 AM #6
Regular Guest
- Join Date
- Oct 2010
- Location
- GREECE
- Posts
- 18
Dear all,
Thank you for your answers and sorry for my English.
By "flooded" I mean that the basement at which the unit is located was full in water.
I found out that there is no official retrofit for CH530 and I decide to replace main switch, CTs, VTs and local cld module.
Everything else will be repaired.
Thank you and best regards,
CV
-
02-21-2012, 08:18 AM #7
Regular Guest
- Join Date
- Jan 2012
- Location
- Perth Down Under
- Posts
- 26
As Tech Rob indicates the liquid level sensor and the exv's will be the problem.
I have never seen this option in the CH-531 retrofit line up either.
The only CH-531 retro that I know off is for gear drive or direct drive conversions. Have done many on the gear-drive machines and are very successful for gathering maintenance information and fault finding. Backup support is hard to come by but I have never needed this requirements
-
02-21-2012, 09:10 AM #8
Professional Member*
- Join Date
- Jan 2008
- Location
- Dallas ,Texas
- Posts
- 3,510