    New to site need help working on 60 ton Trane chilled water air handler. System is over cooling occupied set point at 70 the effective set point shows 40 can't figure out why. Any help greatly appreciated.

  2. #2
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,905
    Post Likes

    Thumbs up



    Or maybe your looking at the offset and the setpoint is 40?
    “It takes courage to grow up and turn out to be who you really are.”

    - E.E. Cummings

  3. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,030
    Post Likes
    Quote Originally Posted by Ctcoffelt View Post
    ...the effective set point shows 40...
    i may not be an expert, but i think that this may be your problem and not the air handler.



    Quote Originally Posted by Ctcoffelt View Post
    ...can't figure out why...
    or it could be this reason.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  4. #4
    Join Date
    Dec 2010
    Location
    New Orleans
    Posts
    1,012
    Post Likes
    Quote Originally Posted by chrishvacman View Post


    Or maybe your looking at the offset and the setpoint is 40?
    And here I was thinking I was a smart arse. Boy you got me beat.. Anyways can't you relinquish the command to go back to the proper setting?

  5. #5
    Join Date
    Jul 2009
    Location
    In a mechanical room....
    Posts
    1,905
    Post Likes
    Quote Originally Posted by keeplearnin View Post
    And here I was thinking I was a smart arse. Boy you got me beat.. Anyways can't you relinquish the command to go back to the proper setting?
    Ive got a hammer that's just big enough to get it back to the proper setting.
    “It takes courage to grow up and turn out to be who you really are.”

    - E.E. Cummings

  6. #6
    Join Date
    Feb 2012
    Posts
    9
    Post Likes
    Thread Starter
    New to site not to hvac not the offset and no cant change it . Supposed to be heat sp + cool sp devided by 2

  7. #7
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    Your profile is kinda slim. No offense, but is English your first language? I ask because I wonder if that is why I don't recognize a couple of things. Is "effective setpoint" the same as "active setpoint"? And I'm not familiar with "tscb", but then I certainly don't claim to have worked on all the Trane air handlers either. Maybe it's a matter of the air handler being in "remote control" or "local control". You may think you have one, when you really have the other.

  8. #8
    Join Date
    Feb 2012
    Posts
    9
    Post Likes
    Thread Starter
    Yes it is the same as active set point on my control module it says effective the tscb is a built air handler it has the tracer ah system I have local zone thumb will enabled

  9. #9
    Join Date
    Feb 2012
    Posts
    9
    Post Likes
    Thread Starter
    Just a little back ground I have been doing hvac for about 10 years worked on carrier chillers here and there but not much this is the first Trane that I have worked on the company I'm doing the work for has always used Trane services so they may have set something up that I can't see been doing a little research wandering if they used the rover to set it up

  10. #10
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    Like I said, I'm not familiar with that unit. If the operator interface is similar to the Intellipak then it could be confusing to understand. Others here may be familar with what you have. Some may "bust your chops" a little bit while waiting for more info, no harm meant, I'm sure. But my first thought was, and still is, a possibility. Also it could be a matter of what sensor is selected for whichever function. Access to an IOM or a programming guide for that unit would probably be a BIG help to you.

  11. #11
    Join Date
    Feb 2012
    Posts
    9
    Post Likes
    Thread Starter
    Just downloaded the tracer manual gonna read up a bit but thanks for your input

  12. #12
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,171
    Post Likes
    You're welcome, and good luck.

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,030
    Post Likes
    does it have the 'blue screen' MP540 touch screen controller?
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.