Results 14 to 20 of 20
    Valdosta Ga
    One of the first jobs I did on a install with Carrier contractor was a tripping cb in heat mode turned out to be a fan relay wired wrong from the factory
    Jan 2012
    Toronto
    Usually motors draw more current upon start up. The induced emf (Electro Magnetic Field) in the motor's shaft depends on the rotation speed of the motor (at startup roter is at rest) so therefore the starting current (called inrush current) will be up to 10 times higher than the motor's rated current.
    I suggest turning the units on one at a time.
    Jan 2012
    indy
    Quote Originally Posted by Tech it out View Post
    Actually had an electrician (experienced with own biz) tell me there was no such thing as a weak breaker!
    anything is possible
    Mar 2012
    My house is in Texas..
    Dumb idea .... But check lug connection on all electrical fittings going to main ...
    "Duct tape is like the force. It has a light side, a dark side, and it holds the world together."
    Mar 2012
    Ps..
    Did it trip when you tested it? What was volts?
    Feb 2012
    Alabama
    Quote Originally Posted by hvacmike85 View Post
    Ive changed many over the years that had no where near the rated amps. Maybe we should start calling it "strength challenged" instead of weak!
    II Chronicles 7:14 Galatians 2:20 Ephesians 2:8-9
    Nov 2011
    East Side
    yeah, what's the LRA ratings on those units?? if they both started at the same time....or if the building amp draw was already high, and one kicked on,that might do it.
    just looked at a 3ton residential rheem yesterday, it's comp. LRA was 112a.