Page 1 of 2 12 LastLast
Results 1 to 13 of 16

Thread: Sizing AC Unit

  1. #1
    Join Date
    May 2001
    Posts
    41
    Post Likes

    Sizing AC Unit - Whole House or Zone???

    We have just had our heating/cooling system zoned into 4 zones using a Honeywell Trol-A-Temp system. We are considering replacing the AC unit which is a 3.5 ton unit with a smaller one. I used the HVAC Calc Residnetial software(Great Program - Very Intuitive and Easy to Use) and came up with a total heat gain for the building as 33,789. The largest heat gain in any of the zones is 16,300. How do we size the AC unit? Since there is a foyer, there will be heat flow between the zone.

    Thank you for the help.



    [Edited by fmwaz on 05-17-2001 at 11:25 AM]

  2. #2
    Join Date
    Jul 2000
    Location
    Ottawa, Ont. Canada
    Posts
    1,729
    Post Likes

    more information

    Hi, I believe there is one more piece of information I would like to add here. I spoke to fmwaz on the phone and he told me that the way the duct zoning works with this system is only one zone gets air at a time and the dampers are down at the furnace essentially blocking off 2 zones as one gets fed. I am not up on the Trol-A-Temp system but if this is correct, I would be concerned about putting in a 3 ton because there wouldn't be enough air flow over the coil. Can somebody with experience with the Trol-A-Temp system please reply and give me an education on how it works?

    Thanks

    don
    don sleeth - HVAC-Talk Founder
    HVAC Computer Systems
    Heat Load Calculation Software

  3. #3
    Join Date
    Nov 2000
    Location
    Ottawa, On. Canada
    Posts
    32
    Post Likes

    Smile Trol-A-Temp

    Originally posted by Don Sleeth
    Hi, I believe there is one more piece of information I would like to add here. I spoke to fmwaz on the phone and he told me that the way the duct zoning works with this system is only one zone gets air at a time and the dampers are down at the furnace essentially blocking off 2 zones as one gets fed. I am not up on the Trol-A-Temp system but if this is correct, I would be concerned about putting in a 3 ton because there wouldn't be enough air flow over the coil. Can somebody with experience with the Trol-A-Temp system please reply and give me an education on how it works?

    Thanks

    don
    I'v never worked on the trol-a-temp system but try this website http://hbctechlit.honeywell.com/.
    Dave

  4. #4
    Join Date
    May 2000
    Location
    Atlanta,GA.USA
    Posts
    210
    Post Likes

    zone

    zoning is basicly, a themostat controls each zone.
    1 2 3
    I'm concered when people want to change there units.
    what if you want all zone's on the 3.5 cooled it all
    if you drop to a 3 ??
    i do get much work for this but have some ask an will
    be getting into it more.

  5. #5
    Join Date
    Apr 2001
    Location
    Arkansas
    Posts
    2,112
    Post Likes

    Hmm

    If his zone system shuts down all zones but one at a time, he's got problem with it. Just as Dependsaservice said the unit is controlled by a master thermostat and the other stats control dampers.
    "FIGHT CRIME: SHOOT BACK"

  6. #6
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    35,197
    Post Likes
    Each stat can bring on the equipment and open the damper for that zone. It is possible for a 3.5 ton unit to be feeding a duct designed for a fraction of that. Therefore, if properly installed, a bypass damper is used to return the excess back to the A/C. With Trol-a-temp's newest panels, they have a thermistor that goes in the supply and monitors for overheat or near freezing conditions to shut off the equipment before a coil freezes or a furnace cycles on limit. If the system does not have a bypass or the Zonemax sensor isn't used, he will have problems.

    As for his gain, seems to me he has a 3 ton heat gain and when the A/C is changed, it should be to a 3 ton.

  7. #7
    Join Date
    Jul 2000
    Location
    Ottawa, Ont. Canada
    Posts
    1,729
    Post Likes

    ah, that makes sense

    Thanks Baldloonie, the bypass damper was the piece of the puzzle I was missing. With that in place, then yes a 3 ton is what's called for or even save the expense and go with the existing 3.5 if it is a good working unit. His contractor was suggesting a smaller unit, I think because of the air flow, so I hope he was aware of the bypass damper. If he wasn't, I am sure he will be shortly

    don

  8. #8
    Join Date
    Jun 2001
    Posts
    3,918
    Post Likes
    Originally posted by r22d22
    Read
    Read What ?

  9. #9
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,050
    Post Likes
    Originally posted by bb
    Originally posted by r22d22
    Read
    Read What ?
    Still lost yet again, but I can relate to your bio. in your profile.

  10. #10
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,050
    Post Likes
    Hey, I like ideas, I even get a couple now and then. What's yours.

  11. #11
    Join Date
    May 2001
    Location
    Kansas City
    Posts
    2,731
    Post Likes
    Originally posted by r22d22
    Originally posted by bb
    Originally posted by r22d22
    Read
    Read What ?

    bb and lynn rodemayer don't know what to read.
    (nothing)
    A windows macro cause me to submit some strange entries without knowing it. But the replies were deliberate.
    This gives me a great ideal.
    Windows macro? Or drugs?

  12. #12
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,050
    Post Likes
    Hey Mr. Smith. Which company do you work for? If you don't want to say, just reply bug off.

  13. #13
    Join Date
    Jul 2003
    Posts
    646
    Post Likes
    "bb and lynn rodemayer don't know what to read.
    (nothing)"

    This is logically incorrect. What your are saying here is BB and Lynn know what to read. (everything)

    Jeff

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event