    E-Link Gateway connection

    1. I have 3 York YK centrifugal chiller and i wan it to be integrated to BMS (BACNet). Do I need to buy 3 E-Link gateways or just 1 and connect the Chiller Controls yorktalk RS-485 in series. The control panel is non-optiview.

    2. Another option on this chiller is replacing the entire control panel with a third party DDC and an Human Machine Interface with local 15" display and operatable by BACNet.

    The Chillers are 20 years old and in good running condition. I want it as modern as possible

    How?

  2. #2
    Join Date
    Mar 2001
    Location
    North Florida / South Georgia
    Posts
    100
    You need 3 e-links, one per machine. They are easy to setup.

  3. #3
    Join Date
    Nov 2005
    Location
    Shreveport, Louisiana
    Posts
    2,338
    Contact your jci rep...