    York VCIV 2 compressor chiller

    Good morning,

    Working on a chiller system control project. Looking to integrate the ddc control panel into the chiller system via a hard wire. I have poured over the wiring schematics and from the looks of things this is not possible. Does anyone have any experience with this.

    thanks in advance

    Cris

  2. #2
    Join Date
    Jan 2008
    Location
    East of big city prices.
    Posts
    3,750
    Post Likes
    Explain hard wired ?

  3. #3
    Join Date
    Jun 2005
    Posts
    10
    Post Likes
    looking to hardwire the start/stop, safeties and modulation.... through the control panel i am building.... and bypass the bms

  4. #4
    Join Date
    Sep 2007
    Location
    Somewhere in the world.
    Posts
    1,643
    Post Likes
    Enable & disable thats all you need to do the Chiller will do the rest (Really)
    A mind is like a parachute. It doesn't work if it is not open.

    The best part of going to work is coming back home at the end of the day.

    Hard work spotlights the character of people: some turn up their sleeves, some turn up their noses, and some don't turn up at all.

  5. #5
    Join Date
    May 2008
    Posts
    14
    Post Likes
    There is alot of hard wire capabilities with this chiller. You need to be more specific about what you , would like to do . ? do you want to reset setpoints , see the status of systems , or alarms . turn on pumps using the outputs . or just turn on individual systems. form 201.23.nm2 (608) part number 035-21506-101 pages 80 and 81 has alot of information on it. I don't know what form you are looking at but look very closely at the electrical diagram section.
    the YCIV 's are alot alike.

  6. #6
    Join Date
    Jun 2005
    Posts
    10
    Post Likes
    Quote Originally Posted by whatusi View Post
    There is alot of hard wire capabilities with this chiller. You need to be more specific about what you , would like to do . ? do you want to reset setpoints , see the status of systems , or alarms . turn on pumps using the outputs . or just turn on individual systems. form 201.23.nm2 (608) part number 035-21506-101 pages 80 and 81 has alot of information on it. I don't know what form you are looking at but look very closely at the electrical diagram section.
    the YCIV 's are alot alike.
    Hello,
    I have the panel schematic drawn up.. I am setting up the ability to start/stop the chiller..... I am using the wiring diagram that you mentioned. But it looks like there aren't any terminals where i can wire in my remote start/stop.... There is run permissive but that looks like it is part of a safety circuit tied in with the flow switch... all set up in series (and configuration) I have the pump request, chiller run, alarm, remote modulation so thats not an issue...

    Oh by the way thanks

  7. #7
    Join Date
    May 2008
    Posts
    14
    Post Likes
    Use the run permissive to enable each system (compressor) !

  8. #8
    Join Date
    Jun 2007
    Location
    Here. I'm right here i tell you!
    Posts
    465
    Post Likes
    Quote Originally Posted by whatusi View Post
    There is alot of hard wire capabilities with this chiller. You need to be more specific about what you , would like to do . ? do you want to reset setpoints , see the status of systems , or alarms . turn on pumps using the outputs . or just turn on individual systems. form 201.23.nm2 (608) part number 035-21506-101 pages 80 and 81 has alot of information on it. I don't know what form you are looking at but look very closely at the electrical diagram section.
    the YCIV 's are alot alike.
    Why make it more complicated. York56 is right.