Thread: vacume pump too big?

  1. #21
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    3,111
    Post Likes
    Quote Originally Posted by tranedog View Post
    Oh BARBAR.... please read all my posts... I stated all the exceptions and minus 10 degrees (F) at 500 microns is the boiling point of h2o (ie WATER)... And TRANEDOG has been MISTAKEN but NEVER WRONG....lol but seriously please re-read all my posts on this subject... please post your apology... Thank you ;-) p.s. DRY ICE is not water.... so there is no relevance to comparing dry ice to water...
    I apologize whole heatedly for any hurt i may have done to your sensibility!
    Technically well that is different.
    Read what you have just written.
    at -10F water does not boil at 500microns, it does however vaporize, during the sublimation process. Which is a solid converting to a vapour(gas) with out going through the liquid stage.
    We see this most commonly with dry ice (solid CO2), H20 (steam/water/ice) does the same thing.
    Study freeze driers, you will find it interesting!

  2. #22
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Paysonhvac had posted a video showing water freezing while under a vacuum. Can't find it right now. But there are a few other ones on utube showing water freezing under a vacuum.

    Its possible, and may happen more often then we think. Such as on those systems that pull down to 400 microns, and then rise to 800 or 900. Then after you pull the vacuum down again another time or 2 it holds. Sublimation will show as a slow rise in vacuum. Often we just take it for granite that it was just moisture(water droplets) trapped somewhere in the system. When it was small ice crystal/crystals sublimating.

    There have been several discussions about this in the Pro tech forum.

  3. #23
    Join Date
    Jul 2006
    Location
    Phoenix, AZ
    Posts
    227
    Post Likes
    Please reference the following website-
    29.92 inch Hg Vac. = 0 microns boiling point of water will be 80 F
    29.90 = 500 microns -10 F
    28.92 = 25401.07 microns
    1” Hg Vac. = 25401.07 microns

    http://www.hvacfun.com/f-vacuum-pumps.htm

    More detail regarding vacuum pump for dehydration of a closed system....

    http://www.robinair.com/acsolutions/...cuum.php#high2
    The BITTERNESS of POOR QUALITY remains long after the SWEETNESS of LOW PRICE is FORGOTTEN.

  4. #24
    Join Date
    Mar 2003
    Posts
    1,234
    Post Likes

    Smile

    [QUOTE=beenthere;12403541]Paysonhvac had posted a video showing water freezing while under a vacuum. Can't find it right now. But there are a few other ones on utube showing water freezing under a vacuum.

    When I do vacuum pump clinics I take a clear glass beaker with about 4 drops of water in the bottom and then hook it up to the vacuum pump and micron gauge and you can watch the water freeze and then eventually go through sublimation if you wait long enough. It is interesting but not necessarily what will happen in a system. I use this example, more than anything, to emphasize the importance of a good evacuation and the use of a good micron gauge. I know there are many other factors to consider but it has sure made an impression on service techs here and also increased my sales of micron gauges.

  5. #25
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    4,043
    Post Likes
    Quote Originally Posted by tranedog View Post
    Please reference the following website-
    29.92 inch Hg Vac. = 0 microns boiling point of water will be 80 F
    29.90 = 500 microns -10 F
    28.92 = 25401.07 microns
    1” Hg Vac. = 25401.07 microns

    http://www.hvacfun.com/f-vacuum-pumps.htm

    More detail regarding vacuum pump for dehydration of a closed system....

    http://www.robinair.com/acsolutions/...cuum.php#high2
    Thanks for the link to that Robinair page. Halfway down the page is a table for the boiling points of water. It is a very useful table and one that all techs should have. That other link is badly misinformed and should be ignored. Not one piece of information you quoted from it is correct. Compare them to the Robinair chart.

  6. #26
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    [QUOTE=woody19;12405781]
    Quote Originally Posted by beenthere View Post
    Paysonhvac had posted a video showing water freezing while under a vacuum. Can't find it right now. But there are a few other ones on utube showing water freezing under a vacuum.

    When I do vacuum pump clinics I take a clear glass beaker with about 4 drops of water in the bottom and then hook it up to the vacuum pump and micron gauge and you can watch the water freeze and then eventually go through sublimation if you wait long enough. It is interesting but not necessarily what will happen in a system. I use this example, more than anything, to emphasize the importance of a good evacuation and the use of a good micron gauge. I know there are many other factors to consider but it has sure made an impression on service techs here and also increased my sales of micron gauges.
    LOL... It is an eye opener when you first see it.

  7. #27
    Join Date
    Jun 2007
    Location
    Central, FL
    Posts
    871
    Post Likes
    My logic is that if you pull the vapor moisture out of the system the LLFD and the SLFD should be able to trap any ice in the system and not allow it to dissipate and become moisture. Also the use of nitrogent whuch is resilient to acids and bases as well as oxidants and most reductants eliminate this problem.
    WARNING:IF YOU DON'T KNOW THEN DON'T DO, SO THOSE WHO KNOW WHAT YOU DIDN'T KNOW DON'T END UP UNDOING WHAT YOU DID SO IT COULD GET DONE RIGHT!

  8. #28
    Join Date
    Dec 2011
    Location
    Northwest Georgia
    Posts
    111
    Post Likes
    Always triple evacuate, its cheap easy insurance

+ Reply to Thread
Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •