    Colorado
    when the AC ran for 1.5 hours yesterday and not one drop of condensate came out the pipe.
    Apr 2006
    Nebraska
    Talking
    ...stopping at the local pub for a pint after a hard day of breakdowns and realizing it's 2 AM.
    "Egotism is the anesthetic that dulls the pain of stupidity."
    Frank Leahy
    Or the drain line is clogged.
    Kingston, Ny
    Check the secondary drain line?
    Check you coil, Is your coil a block of ice?
    Check your pressures?
    Check your SH or SC?
    Check the drain line, is it cracked somewhere in line?
    Check the filter(s)
    Check check check... Is this thing on?
    May 2002
    Colorado
    Line is clear and everything is OK. Indoor RH yesterday afternoon was below 30% even before the AC came on. Outdoor RH was about 10% most of the afternoon.
    Jan 2005
    Central Fl
    What was the dew point of the indoor air? What was the saturation temperature of the refrigerant?
    South Dakota
    In order for moisture to condense on the coil the coil temperature must be at or lower than the dew point temperature of the air.
    Using a psychrometer measure the wet and dry bulb temperatures of the air and find the stat point on a psychrometric chart. Then, plot the dew point of the room air and compare it to the coil temp.
    The coil temp must be the same or lower than the dew point temp of the air for condensation to occur.
    [Edited by NormChris on 04-16-2006 at 12:55 AM]
    May 2002
    Colorado
    The indoor dew point was about 38F.
    SW FL
    Right
    I didn't know Panama would be that dry in April.
    at 10% R.H., A/C is not needed < 100'F.
    Designer Dan