    Heat pump temp. output at registers normal?

    Hi, I have a Lennox XP17 2.5 Tand installed a year ago. Just wondering in my temperature output at the registers is just about normal.

    With heat pump running and no heat strips engaged, I am receivng a temp of 80 degrees at the registers.

    conditions:

    house temp: 68F
    outside air temp:14F

    Is 80 that I am receiving at the registers normal or am I below what it should be??

    tks

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,074
    At a brisk 14 out, 12 rise may not be too bad. Probably losing a little in the ductwork too. More accurate is taking a reading entering the blower and a couple feet away from it to take duct loss out of the equation. Doing it both ways alerts you to the duct loss.

  3. #3
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    798
    12 degree rise at 14 odt sounds pretty good to me BUT it may make more sense, economically, to run the strip heat at that temp. Any Trane guys have guys have performance data for this machine?

  4. #4
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,898
    Quote Originally Posted by Gross View Post
    12 degree rise at 14 odt sounds pretty good to me BUT it may make more sense, economically, to run the strip heat at that temp. Any Trane guys have guys have performance data for this machine?
    Whats Trane got to do with a Lennox heat pump.

    It would make no sense to witch to emergency heat. The strip heat would cost more to use then the heat pump.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Jul 2004
    Location
    Massachusetts
    Posts
    6,837
    Quote Originally Posted by Gross View Post
    12 degree rise at 14 odt sounds pretty good to me BUT it may make more sense, economically, to run the strip heat at that temp. Any Trane guys have guys have performance data for this machine?
    Why Trane, he said it's a Lennox system?? To me, the real question is whether the HP is keeping up with the set-point. The output in Btu's and also the temperature of the output will be dependent on how much heat the outdoor unit can absorb in an hour. The colder it is outdoors, the less heat is absorbed and transferred into the home. Since a Btu is a measure of heat, a dropping supply temperature goes hand-in-hand with the output of the HP. When balance point is reached (HP running constantly and just maintaining t-stat set-point) then the HP supply temp is at the lowest. Below balance point requires the addition of Btu's to heat your home. The use of electric resistance heat will boost the supply air temps as more Btu's are delivered into the home.
    If YOU want change, YOU have to first change.

    If you are waiting for the 'other guy' to change first, just remember, you're the 'other guy's' other guy. To continue to expect real change when you keep acting the same way as always, is folly. Won't happen. Real change will only happen when a majority of the people change the way they vote!

  6. #6
    Join Date
    Jul 2006
    Location
    Virginia
    Posts
    4,624
    @ 14 degree outdoor temp a 12 degree temp rise seem pretty good to me just let the thermostat add auxillary heat as needed and let that heat pump run.

  7. #7
    Join Date
    Aug 2011
    Location
    Eastern Shore, MD
    Posts
    798
    Quote Originally Posted by beenthere View Post
    Whats Trane got to do with a Lennox heat pump.

    It would make no sense to witch to emergency heat. The strip heat would cost more to use then the heat pump.
    It has nothing to do with Trane. I saw an X and stopped paying attention.

    But thanks for calling me out. I'll gladly post links to other threads I've made simple errors in if you'd like to continue to critique?

  8. #8
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,898
    Quote Originally Posted by Gross View Post
    It has nothing to do with Trane. I saw an X and stopped paying attention.

    But thanks for calling me out. I'll gladly post links to other threads I've made simple errors in if you'd like to continue to critique?
    I probably already saw those post. But left you slide on them. LOL
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  9. #9
    Join Date
    Feb 2012
    Location
    Michigan
    Posts
    87
    Quote Originally Posted by catmanacman View Post
    @ 14 degree outdoor temp a 12 degree temp rise seem pretty good to me just let the thermostat add auxillary heat as needed and let that heat pump run.

    Now you've got me thinking about ditching propane and going all electric with air source HP.

    Many of the systems I've been looking at are claiming 1.5 COP at -10F, when I'd always thought HPs were useless under +20F.
    I assume the electric strips are downwind of the heat pump's coil and both can run together, but by -10F the HP is contributing a lot less heat than the auxiliary strip , so the overall COP is slightly over 1?