    Somebody would know the formula for calculating phase imbalance!!!

  2. #2
    Join Date
    Apr 2005
    Location
    where the beer flows like wine
    Posts
    2,871
    check this link http://www.welchnet.us/industrial/drivesandpower.html
    there is plenty more over in the training and eduction forum http://www.hvac-talk.com/vbb/forumdi...=31&daysprune=

  3. #3
    Join Date
    May 2004
    Posts
    1,865
    Percent imbalance = maximum deviation from average /
    average of three phases X 100%
    Example:
    1. As measured: Phase A = 449 A; Phase B = 470 A;
    Phase C = 462 A
    2. Calculate Average = (449 + 470 + 462) / 3 = 460 A
    3. Calculate Max Deviation = 460 449 = 11 A
    4. Calculate Imbalance = (11 / 460) x 100 % = 2.4 %

    http://support.fluke.com/educators/d...161031_b_w.pdf