  1. #1

    Unhappy Help with Coleman HP

    We got a 14seer Coleman Echelon in 2007 and it has worked pretty well. All of the sudden if I try to run the AC the outdoor unit turns on for about 1-2 min and shuts off.

    I cleaned the outside coils today and noticed a fault light for a low pressure lock out.

    What does that mean.
    Could I have set something improperly in my tstat?
    Heat and Em heat work fine.

    Thanks for all help.

  2. #2
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Is it cold out?

    Best to call your HVAC company.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  3. #3
    It has been between 50 and 80.

    The past month it has gotten into the 20-30 range.

  4. #4
    FYI

    Its a Coleman HC5B036F1B with a Climatouch CT03ts32H tstat. I can get the info on the attic unit

  5. #5
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Quote Originally Posted by noleguy83 View Post
    It has been between 50 and 80.

    The past month it has gotten into the 20-30 range.
    I meant was it cold out when you turned on the cooling.

    Sounds like you may have a leak in the system. You really do need someone who knows what they are doing check it out. If the system is shutting down on low pressure issues, something is wrong that needs to be fixed or it is going to get much worse.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


  6. #6
    Thats what I was told I just wanted to make sure before the repair guy could pull one over on me. I just was shocked that a 5yr old unit could have a leak.

    Are there any other things that could cause this issue?

    Thanks!

  7. #7
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,808
    Quote Originally Posted by noleguy83 View Post
    Thats what I was told I just wanted to make sure before the repair guy could pull one over on me. I just was shocked that a 5yr old unit could have a leak.

    Are there any other things that could cause this issue?

    Thanks!
    Yep, sounds like the repair guy may be on track. Parts should be in warranty.
    Life is too short, Behappy!
    TFMM

  8. #8
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    68,923
    Quote Originally Posted by noleguy83 View Post
    Thats what I was told I just wanted to make sure before the repair guy could pull one over on me. I just was shocked that a 5yr old unit could have a leak.

    Are there any other things that could cause this issue?

    Thanks!
    Lots of things could be going on. A blockage in the system could give the same symptoms. If I had to make a WAG, I'd be willing to bet there is a txv on the indoor coil that is being a bad boy.
    Government is a disease...
    ...masquerading as its own cure…
    Ecclesiastes 10:2 NIV


Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event