Thread: purge on cvhe
-
02-02-2012, 11:03 AM #14
Professional Member*
- Join Date
- Dec 2008
- Location
- Dixiana, AL
- Posts
- 2,487
This is an open forum, folks, not a DIY site. It's getting a little deep wouldn't you agree?
-
02-02-2012, 12:24 PM #15
r-123 removed from the centrifuge, place a blank flange instead of the rupture disc and pressure up to 20psig,
-
02-02-2012, 12:37 PM #16
Professional Member
- Join Date
- Jan 2007
- Location
- cypress, tx.
- Posts
- 95
thanks
yeah Klove is probably right - I got my question answered, which was have you guys seen this before. We'll figure it out eventually - thx for the input.
-
02-02-2012, 08:37 PM #17
Purge purging problems
Guys I know you wanted to close the thread, but Trane did have a service bulletin about this very problem with the purge going into pump-out erroneously. Yes, it does the 18*F and 23*F pump-out start and stop, but it is not caused by a chiller leak. I don't remember what the SB number is. If you were able to achieve that vacuum level it is not chiller related. I am sure any of out profound Trane techs could locate it. Good Luck- GEO
Of all the things I have lost in my life, I miss my mind the most-GEO
-
02-02-2012, 09:37 PM #18
Professional Member
- Join Date
- Sep 2011
- Location
- Northwest Louisiana
- Posts
- 152
Floats stick and drain back lines clog with rust and other crud. been there, done that.
A LITTLE BIT OF STUPID GOES A LONG WAY!
-
02-02-2012, 09:51 PM #19
Professional Member
- Join Date
- Jun 2010
- Location
- Tampa, FL
- Posts
- 96
Also check the pump out pump to make sure it pulls a decent vacuum say 25" min. I have seen cracked diaphrams and dirt or teflon tape in the reed valves. Make sure solenoids seat tight. Sometimes air comes right back in the pump out line.
-
02-02-2012, 10:12 PM #20
Professional Member
- Join Date
- Sep 2008
- Location
- A land down under
- Posts
- 285
Necessity is the mother of invention
-
02-02-2012, 11:34 PM #21
Bad email address, please contact Admin to fix
- Join Date
- Sep 2011
- Posts
- 18
If you leak check again check the threads on float of the purge. They tend to leak worse as the purge cylinder cools down. If you are running then hopefully it is in a positive pressure or close to it but if chiller was shut down tank could fill with air rather quickly. I've pulled vacuum alot of times just to have this cause leak check to fail. No, about the third time it happen I decided to pull the float on every rebuild and liberally apply teflon tape to try to resolve.
-
02-04-2012, 10:14 AM #22
Pull the purge into a vacuum and see if it holds.
Federal Reserve, stealing your kids futures since 1913
UA290
-
02-04-2012, 12:07 PM #23
This may be stating the obvious, but if chiller is truly "leak free", purge is not needed. Having cut my teeth on R-11 units, I've found 123 units to be mystifying. The refrigerant just does not behave the same. Leak testing and purging can both be exasperating. Post does not specify operating mode selected or if purge operation is as frequent with chiller running or idle, items that would tend to steer my diagnosis towards either a leak in the chiller or an ineffective purge unit.
-
02-05-2012, 11:14 AM #24
Professional Member
- Join Date
- Jan 2007
- Location
- cypress, tx.
- Posts
- 95
Thx for the SB - pretty sure I've covered most of it except #8 - vapor or liquid connections below the liquid level in the chiller condenser - and maybe a leak after the solenoid(s). They were running the condenser water way below design when I walked up on this one ( bypass actuator control line reversed), so it's not hard to believe that they were stacking in the condenser;however, that was corrected before charge was pulled, so connections should be above the liquid level. Havent been on this one since Weds., but I'm told that the contractors pulled a vacuum on the purge which didn't hold, and have declared thier theory about the 134a leaking into the tank to be the cause of the problem. If the PO hasnt been issued for a new purge, I'm gonna pressurize the purge. Gotta be a leak there somewhere.
-
02-13-2012, 09:41 AM #25
Regular Guest
- Join Date
- Jan 2012
- Location
- Perth Down Under
- Posts
- 26
In your first statement you said the machine lost 300 lbs of refrigerant. This would indicate the leak is on the high side of the machine where ever the refrigerant was positive. If on the low side then it would have sucked in air only. Was the unit leaked checked while running? Just because it holds a vacuum does not mean it does not leak. Check solenoid valves, gaskets etc.
Does the purge leak purge more when first started and less and less as the machine runs (indicates leak is on the high side) or does it purge all the time indicating the leak is on the low side.
If the purge was loosing the R134a to the chiller then it would not purge at all as the suction temperature would not drop as there is no heat transfer in the purge tank.
-
02-20-2012, 01:51 PM #26
Purge soleniods are common leakers. The purge orifice could be plugged up not allowing it to vent.
" Guess I will have to bust out my brand new Meriman mercury manometer!""I'm from Texas, what country are you from?"