    r-123 removed from the centrifuge, place a blank flange instead of the rupture disc and pressure up to 20psig,

  3. #16
    Join Date
    Jan 2007
    Location
    cypress, tx.
    Posts
    105

    thanks

    yeah Klove is probably right - I got my question answered, which was have you guys seen this before. We'll figure it out eventually - thx for the input.

  4. #17
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    880

    Purge purging problems

    Guys I know you wanted to close the thread, but Trane did have a service bulletin about this very problem with the purge going into pump-out erroneously. Yes, it does the 18*F and 23*F pump-out start and stop, but it is not caused by a chiller leak. I don't remember what the SB number is. If you were able to achieve that vacuum level it is not chiller related. I am sure any of out profound Trane techs could locate it. Good Luck- GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  5. #18
    Join Date
    Sep 2011
    Location
    Northwest Louisiana
    Posts
    290
    Floats stick and drain back lines clog with rust and other crud. been there, done that.
    A LITTLE BIT OF STUPID GOES A LONG WAY!

  6. #19
    Join Date
    Jun 2010
    Location
    Tampa, FL
    Posts
    101
    Also check the pump out pump to make sure it pulls a decent vacuum say 25" min. I have seen cracked diaphrams and dirt or teflon tape in the reed valves. Make sure solenoids seat tight. Sometimes air comes right back in the pump out line.

  7. #20
    Join Date
    Sep 2008
    Location
    A land down under
    Posts
    314
    Quote Originally Posted by ga1279 View Post
    Guys I know you wanted to close the thread, but Trane did have a service bulletin about this very problem with the purge going into pump-out erroneously. Yes, it does the 18*F and 23*F pump-out start and stop, but it is not caused by a chiller leak. I don't remember what the SB number is. If you were able to achieve that vacuum level it is not chiller related. I am sure any of out profound Trane techs could locate it. Good Luck- GEO
    That would be PGRC-SB-2, unexplained purge pumpout was an issue on some pre 1997 purifyer purges. The bulletin does run through some of the causes for pumpout occurring without non-condensables in the chiller, most are covered in the preceding threads.
    Attached Files Attached Files
    Necessity is the mother of invention

  8. #21
    SFTB is offline Bad email address, please contact Admin to fix
    Join Date
    Sep 2011
    Posts
    18
    If you leak check again check the threads on float of the purge. They tend to leak worse as the purge cylinder cools down. If you are running then hopefully it is in a positive pressure or close to it but if chiller was shut down tank could fill with air rather quickly. I've pulled vacuum alot of times just to have this cause leak check to fail. No, about the third time it happen I decided to pull the float on every rebuild and liberally apply teflon tape to try to resolve.

  9. #22
    Join Date
    Jan 2004
    Posts
    1,176
    Pull the purge into a vacuum and see if it holds.
    Federal Reserve, stealing your kids futures since 1913

    UA290

  10. #23
    Join Date
    Feb 2008
    Location
    Second City, USA
    Posts
    61
    This may be stating the obvious, but if chiller is truly "leak free", purge is not needed. Having cut my teeth on R-11 units, I've found 123 units to be mystifying. The refrigerant just does not behave the same. Leak testing and purging can both be exasperating. Post does not specify operating mode selected or if purge operation is as frequent with chiller running or idle, items that would tend to steer my diagnosis towards either a leak in the chiller or an ineffective purge unit.

  11. #24
    Join Date
    Jan 2007
    Location
    cypress, tx.
    Posts
    105
    Thx for the SB - pretty sure I've covered most of it except #8 - vapor or liquid connections below the liquid level in the chiller condenser - and maybe a leak after the solenoid(s). They were running the condenser water way below design when I walked up on this one ( bypass actuator control line reversed), so it's not hard to believe that they were stacking in the condenser;however, that was corrected before charge was pulled, so connections should be above the liquid level. Havent been on this one since Weds., but I'm told that the contractors pulled a vacuum on the purge which didn't hold, and have declared thier theory about the 134a leaking into the tank to be the cause of the problem. If the PO hasnt been issued for a new purge, I'm gonna pressurize the purge. Gotta be a leak there somewhere.

  12. #25
    Join Date
    Jan 2012
    Location
    Perth Down Under
    Posts
    26
    In your first statement you said the machine lost 300 lbs of refrigerant. This would indicate the leak is on the high side of the machine where ever the refrigerant was positive. If on the low side then it would have sucked in air only. Was the unit leaked checked while running? Just because it holds a vacuum does not mean it does not leak. Check solenoid valves, gaskets etc.
    Does the purge leak purge more when first started and less and less as the machine runs (indicates leak is on the high side) or does it purge all the time indicating the leak is on the low side.
    If the purge was loosing the R134a to the chiller then it would not purge at all as the suction temperature would not drop as there is no heat transfer in the purge tank.

  13. #26
    Join Date
    Jul 2006
    Location
    The Great country of Texas
    Posts
    429
    Purge soleniods are common leakers. The purge orifice could be plugged up not allowing it to vent.
    " Guess I will have to bust out my brand new Meriman mercury manometer!"
    "I'm from Texas, what country are you from?"

Page 2 of 3 FirstFirst 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event